Yet another thing I can't get my head round - :smug2:
I'm obviously missing something apart from hair and more than a few little grey cells.
When I size up the consumption on the new bungalow I get the following rough consumption figures.
Total possible load - everything switched on at same time - 190 Amps
Worst estimated case - actual - 96 Amps. That's with 3 air cons, oven, 1 water heater and some odds and ends (kettle, TVs, etc.).
However my supply will only be 30 Amps so how does everything still work? 30 Amps is only 7 KW.

My own house has similar electrical stuff and the same supply but we have no problem with overloading.

I've read comments about diversity but even then I can't see how the supply can balance the load.
 
Sure you've done your maths right as 190A seems a big demand for a domestic bungalow, even if you've got power hungry aircons trying to fight against the roaring electric oven!

But if you're right and your supply fuse is 30A (check you've got one?) then if you are actually drawing more than 30A for any significant time that fuse should 'pop'. It certainly shouldn't be letting you draw 96A for any length of time! If it isn't 'popping' then the likelyhood is that when you have things running as per 'normal', you aren't drawing more than 30A!

You can check what you're actually drawing from the supply with your appliances on using a clamp meter to give you a better indication of your current usage.
 
Probably over pessimistic with some of the socket loads so I've made some changes. Total load is now 140 Amps.Total of Air Cons, Oven and Water Heaters is still 85 Amps though and I would expect most of them to be on some time or another.
Supply fuse (I think) is in the meter. I know one small unit in the village had a 63 Amp manual switch to connect to the supply (standard in almost all poorer type Thai houses). The guy there shorted something out and the meter blew.
As I said my own house (next door to new bungalow) has similar electrical equipment (Air Cons, Water Heaters, et.) and don't have any problem with the supply even though we run a lot of stuff together.
 
Calculating maximum demand just by using appliance and equipment KW ratings, can very easily give you false and/or way off the mark values, ...even in the UK. Even easier when you include 3 or 4 heating/cooling aircon units from 9000 to 24000 btu... lol!!

The fact is, none of those items mentioned are going to be continually on together for any amount of time drawing their maximum load. Certainly the Cooker, Heaters, Air-cons and the like, will all be switching on and off. In effect, you will only see a fraction of the installations connected load being drawn at any one time and for more than a few minutes...

You have witnessed all this yourself in your own house, with roughly the same appliances/equipment, etc, without any of the expected nuisance tripping!! Diversity works, and it works extremely well too ...lol!!
 
Most circuit breakers and fuses will handle 3 or even 4 times their rated current for several minutes without blowing or tripping.
 
Calculating maximum demand just by using appliance and equipment KW ratings, can very easily give you false and/or way off the mark values, ...even in the UK. Even easier when you include 3 or 4 heating/cooling aircon units from 9000 to 24000 btu... lol!!

The fact is, none of those items mentioned are going to be continually on together for any amount of time drawing their maximum load. Certainly the Cooker, Heaters, Air-cons and the like, will all be switching on and off. In effect, you will only see a fraction of the installations connected load being drawn at any one time and for more than a few minutes...

You have witnessed all this yourself in your own house, with roughly the same appliances/equipment, etc, without any of the expected nuisance tripping!! Diversity works, and it works extremely well too ...lol!!

Many thanks. Understand now. Too used to the idea of things being either On or Off absolutely. Completely overlooked the auto switching on and of.
 

Reply to Amps - Consumption v Supply in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
998
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
I don't normally get involved with domestic work but this job is for a family member so I cant Simpley say no. the house is a large property with...
Replies
3
Views
1K
Hello, I am getting a bit bogged down with detail as I always try my best to meet every best practice but I am very out of practice as I have...
Replies
6
Views
3K
S
Hi there I'm working in a pizza take away doing the installation for it . Just recieved The kitchen appliances rundown and now planning my final...
Replies
8
Views
6K
Specialist
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock