Big solar
as I understand it, and as I say I do have a conceptual problem with this, if there is a short between the DC and the frame, that frame will hold a potential. it will continue to hold that potential until it is given a path to earth, through a bonding cable if present, or the window cleaner if it isn't!!

Surely there will still be zero potential to earth?
 
All elasatictrickery wants to do is get back to it's point of origin.

If a DC pos is touching the array frame, it will do nothing untill it finds the DC neg of the source. It can't flow until that path is made.

This is why bonding DC down to ground is frowned upon, in doing that, you are creating a path.

It isn't frowned upon - it is a necessity on TL inverters.

Beyond taking an earth outside of the equipotential zone, I can't see why it should be a problem.
 
I avoid transformerless inverters if I can 'cos of the aggro of running an earth

That surprises me. We rarely use anything other than TL inverters if we can help it. The increase in efficiency is significant and it doesn't take long to bond the frame.
 
Biggsolar - as well as bonding the array frames, if required, are you earthing the array frames? i.e down to separate earth spike for TN-C-S or back to main earth for other earthing systems?
 
As far as I can see, you are bonding the array and not earthing it. Earthing, unless I'm somehow mistaken, would have no effect whatsoever as the DC voltage will always be present.
 
So you are bonding back to a separate earth spike or back to the MET (depending on existing earthing system)? I am sure it is me who is mistaken when referring to earthing!
 
back to spike or MET depending on earthing system (much to some electrician's dismay! - Malcomsanford).

The Dti guide mixes up earthing and bonding and to be fair I think most electricians mix the terms up. I'm sure I often say "earthing the array" when what I actually mean is "bonding the array".
 
Thanks biggsolar. I will and have been continuing to bond the array frame back to spike or MET as we mainly use transformerless inverters. But as suggested on this post, my concern was that it could potentially (no pun intended!!) do more harm than good.
 
Reading this thread initially prompted me to unbond my array; read some more of this thread and then went and re-bonded it;now to be on the safe side I have half of it bonded and half un-bonded.

Damn, this thread is hard to follow!
I hope my system is hazard-free:
TL inverter
array bonded (earth wire connects each of the four rails)
earth wire connected all on its own down to a brand new earth spike.
 
  • Like
Reactions: 1 person
The upshot of all this is there are pro's and cons to both sides of arguments reference earthing the array with tranformerless inverters. It comes down to everyones own judgement for each different site. some might say earthing array to electrode is good in event ac gets onto frames etc, others would say if u have an ac 30mA rcd protecting the ac pv circuit any earth fault current over 30mA will isolate the supply and protect the 'window cleaner', some would say that earthing the array just increases likelihood of lightning strikes due the earth grounding. The nic tech guys we spoke to said if u have minimised the risk by: installing an ac rcd to pv circuit, using a transformerless inverter which has an in built protection which would not allow ac into the frame in event of fault and the panels are double insulated are you really gaining anything by earthing the array other than creating a higher potential for lightning strikes etc. The chances of the frames becoming live with ac is very slim with all the above things in place. u just need to ensure u have civered yourself in the event of an incident and as said before there are pros and cons for earthing and not
 
I would disagree with the statement ''The chances of the frames becoming live with AC is very slim"" and suggest you check the voltage from the array frame to earth rod/Met when using a TL inverter
I've checked this on most of the Tls I've installed which is a fair amount and found that on good days the voltage has been upto 126v down to 56v Ac (this does seem to vary with different makes of panels )being the lowest on an overcast day so in my opinion it's a good idea to follow the manufacturers guidance and bond Tl's ,and I also advise customers to turn the array off when cleaning just in case the bonding connection should ever be compromised as the Ac potential vanishes as soon as the system is turned off

Also most Tl's will normally have residual currents upto 50mA and with some over ,this is why you should'nt use 30mA Rcd's
 
u got more chance of killing urself keep messing with ur array!! best stop reading this and leave it to the EXPERTS!!!! let me no when u find one:))))))))))))))))))) u makes ur choice takes ur chances!! or do what some senior members do in there spare time wrap urself in PVC (safe as houses) if not bit swetttty:)
 
Interesting thread....

"Also most Tl's will normally have residual currents upto 50mA and with some over ,this is why you should'nt use 30mA Rcd's" - important observation. As is Edexlab's comments about PV arrays having a potential difference present when using TL inverters.

PV arrays will generate parasitic capacitive leakage currents (AC) naturally, especially when there is dew/moisture present in the mornings and things start to warm up. Combine this leakage current with anything inherently produced by the TL inverter and you can often "nuisance" trip a 30mA RCD. This is why SMA, Fronius, PowerOne etc recommend the use of a minimum 100mA trip limit RCD (300mA for PowerOne I think) when fitting their TL inverters. Whether this requirement conflicts with a pre-determined need to fit a 30mA RCD in compliance with wiring regs/BS standards (indirect contact fault protection, for example) is a debatable point.

Interestingly enough, I did hear that bonding your array to earth can exascerbate the generation of capacitive leakage currents by the array.

Btw, these slowly rising capacitive leakage currents can often not be detected by an internal RCMU (residual current monitoring unit) in the inverter as RCMU's typically only identify sudden rises in leakage current and will often not result in disconnection until max 300mA is reached. Relying on the inverter's built-in RCMU to act as a circuit protective (safety) device should not be recommended.

In addition to these naturally generated capacitive leakage currents, if a component of that leakage current is pure DC, with any greater than 6mA amplitude, a Type-A RCD manufacturer cannot guarantee that the RCD will continue to operate within it's required trip characteristics (required as a safety device to conform to its own standard/Reg 133.1.3). Some Type-A RCDs have been seen to have operated up to 30% over their intended trip limit when such DC leakage current components exceed 6mA pure DC. Type-AC RCDs will simply find themselves with a saturated trip coil and will NEVER trip, under fault conditions.

Anyway, I digress somewhat....my take on it is somewhat like this: If you have a TT supply, don't use a TL inverter - or if you can't mitigate against the BS7671 requirement for a 30mA RCD, don't use a TL inverter unless you can ensure that a 30mA Type-B RCD will function without nuisance tripping. If you can use a TL inverter, earth the array and fit a Type-B RCD for AC and DC circuit leakage fault protection. If you're concerned about the risk of lightning strikes then follow the risk assessment (as part of the recent BS7671 443 ammendment) and fit Type2 SPDs to the DC and AC circuits. If an LPS (lightning protection system) is already in place (or you have a TT supply) then fit Type1/Type2 SPDs accordingly depending on whether adequate separation distances are respected from the LPS and the array frame.

See here and here and here for some info that you may (or may not) find useful,

Andy

(don't shoot me if I've completely hijacked the thread, my apologies, it's been a long day and I'm a wee bit tired so apologies if the above makes no sense at all!) :)
 
  • Like
Reactions: 1 person
Aye, he's an intersting fella, knows his acorns! had a long chat with him the other day about RCDs and in particular about TT systems and RCDs IIf you remember andy we discussed wether a 100ma RCD was adequate on a TT supply if there was no other requirement for a 30ma RCD)
 
Lol, indeed, I missed that point but was reminded by Bruce's comment on another thread, cheers
 
All mcs approved panels are class 2 double insulated. The dc cabling is also double insulated. For this reason I wouldn't earth the mounting system any more than I would earth metal guttering or tv aerial bracketry.​
 
All mcs approved panels are class 2 double insulated. The dc cabling is also double insulated. For this reason I wouldn't earth the mounting system any more than I would earth metal guttering or tv aerial bracketry.​

I would suggest you read some of the threads regarding this subject if you have'nt already done so ,and the DTI guide and BS7671 is worth a look, and Siberts post above
and instead of assuming that it'll be ok you can test a TL array to earth and if you're happy not earthing it then good luck, and you'd better hope no one ever climbs a aluminium ladder to fix/replace the aerial (or clean the panels) and makes contact simultaneously with the array and ground
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Array frame earthing
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
37

Thread Tags

Advert

Thread statistics

Created
paulsamuel1984,
Last reply from
edexlab,
Replies
37
Views
6,290

Advert