Hello,
I know that for 4-20ma transmitters twisted pair cable should be used with the screen grounded at one end only. However for digital signals ( limit switches , push buttons ) can 2 core/ part of a multi core cable be used ?

Thanks
 
Hello,
I know that for 4-20ma transmitters twisted pair cable should be used with the screen grounded at one end only. However for digital signals ( limit switches , push buttons ) can 2 core/ part of a multi core cable be used ?

Thanks
No in my opinion your cable needs to be twisted, shielded and grounded at 1 end to ditch spurious interfering signal, had one problem whereby an AC compressor stopping and starting tripped the UPs control circuit , took me a while to suss the problem, sorted in the end by using a twisted shielded pair for the control circuit, pleased with myself to say the least, boss man was happy as well.
 
  • Like
Reactions: pc1966
Hello,
I know that for 4-20ma transmitters twisted pair cable should be used with the screen grounded at one end only. However for digital signals ( limit switches , push buttons ) can 2 core/ part of a multi core cable be used ?

Thanks

All depends on the environment the cable is installed in.
And what voltage you are using for the signal.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable query
Prefix
N/A
Forum
Electrical Engineering Chat
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
Lc1,
Last reply from
Lc1,
Replies
3
Views
1,654

Advert