Would this single cable come from the spare 32A breaker on my existing board as this wouldn't be enough? I like to understand what's happening and having done a little bit of looking I've seen that henley blocks are used to install sub-consumer units?
Ideally you don't want the kitchen CU off your existing RCDs as the leakage on those ovens is likely to trip it taking out the kitchen and some of your home supply.

If your CU allows internally a 63A (or maybe 50A) MCB off the direct supply (i.e. from main switch to RCD input, not RCD outputs) then it would be better, but still not offering much selectivity. In other words if you have a big fault on one kitchen circuit it will also trip the supply MCB taking out all of the kitchen electrics. So don't put your lights on it with this configuration as that would be very dangerous. Probably you should look at some sealed "non corrosive" LED strip-lights with built in emergency backup anyway, just in case you are running lots of hot appliances and the mains fails plunging you in to darkness.

That is why the usual suggestion is to split the tails feeding your main CU (where the Henley blocks come in) and then have a fused-switch to feed the sub-main cable to the 2nd CU. The selectivity between a 63A fuse and something like a 20A MCB or RCBO for the cookers is quite good so a fault would be localised to the final circuit.

Generally you should have all of the final circuits on RCBO if you can, though if the ovens are hard-wired (e.g. FCU) and the cables not buried < 50mm they could have RCD protection omitted. Socket outlets should always have RCD protection.
 
Last edited:
You really need to list every single item with their rated values. You also need to advise what sort of loads the normal household has. ie electric showers - how many, car charging points, current domestic kitchen set-up etc. What hours would the business side run, could you honestly run the business side and near enough shut off the living arrangements at the same time? If not it looks like there may be a possibility of a total power outage at some stage.
 
The total mentioned above is 58A without allowing any diversity (I would be cautious about how much is allowable for commercial kitchen?).

So long as no showering and no big EV charging during working hours they may be OK on a normal supply, but wise to check if it is 60/80/100A.
 
The total load was 58 amps before the electric oven was mentioned/added, no mention of a possible microwave?
It really needs someone to visit site and make a proper evaluation.
Yes, I should have read it more carefully as the oven (probably 10-15A) and dishwasher (same again?) all pushes up the peak demand.

If they have 100A (or can get upgraded to it) then it is looking OK, but dodgy for a 60A supply.
 
Out of curiosity I looked up to OSG table A2 for diversity on non-domestic cooking and it suggests:
  • 100% of max demand appliance +
  • 80% of next biggest +
  • 60% of the rest.
Here they are all roughly the same so it is leading to around a 70% overall factor taking 58A to 40A-ish. but the concern would be at start of they day putting on all fryers to get them to temperature and maybe a coupler of other things as well.
 

Reply to Commercial kitchen from home in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
704
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Looking for some advice on what I've discovered is the electrics situation in my rental property. I'll note that before I moved in here I made...
Replies
118
Views
11K
Hi all, I am undertaking a partial rewire of a house that a client is needing to do quite a bit of surgery on as tenant just left and what a mess...
Replies
10
Views
2K
Hello again Thanks to those who answered my question on PIR/occupancy sensors for my downstairs toilet. I have some questions regarding a flat...
Replies
17
Views
4K
specs
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock