Situation: Full rewire of a house, The distribution board is located in the garrage on the adjacent wall back to back with the house.. The roof level of the garage is below the ceiling of the joists so can't break threw at high level

It's my intention to run the cables down/up the internal wall and punch threw into the back of the garage D.B..

Question: The cables are not in ' permitted cable routes' as per the regs fig 3 (150mm ruling) .. I was going to sink the cables and plate over with one 3/4mm Steel and earth it as a means of mechanical protection..

all circuit RCD protected..

Doing the above I must meet the requirement below:

522.6.6 A cable concealed in a wall or partition at a depth of less than 50 mm from a surface of the wall or partition shall: (i) incorporate an earthed metallic covering which complies with the requirements of these
be mechanically protected against damage sufficient to prevent penetration of the cable by nails, screws and the like,

Any thoughts ??

Jon
 
Do the cables need to be buried? I would bet the distance you talking about isn't far. One solution would be to put some PVC trunking in to where you need to punch through, not an ideal method but less hassle and you use some decent trunking finishing it off with an end cap, just a thought.
 
Nothing wrong with covering the cables with 3/4mm steel plate.
There is no requirement for the steel plate to be earthed.
 
Do the cables need to be buried? I would bet the distance you talking about isn't far. One solution would be to put some PVC trunking in to where you need to punch through, not an ideal method but less hassle and you use some decent trunking finishing it off with an end cap, just a thought.

Thanks for your reply..trunking is not an option as it's in the main hallway adjacent to the door
 
Or put the CU somewhere else :). As an aside, never like em in garages, going out in the middle of the night tripping over things to reset the flipping rcd.

PS would you plaster over the steel plate?
 
spinlondon is correct re no need to earth a steel protective plate. wilko's idea is genius.
 
Bet someone still comes along and puts a shelf above though :rolleyes:
 
Or put the CU somewhere else :). As an aside, never like em in garages, going out in the middle of the night tripping over things to reset the flipping rcd.

PS would you plaster over the steel plate?

Yes- skim finished..I agree about putting not putting them in garage..I was thinking of installing an EM light put that opens another box of worms!!!
 
possibly find the existing cables enter the cavity and go up a couple of feet then come out under floor. if so, they could be used as draw wires.
 
  • Like
Reactions: Vortigern
Cables in cavities, whatever next. Let the cavity debate begin :rolleyes:
 
  • Like
Reactions: DPG and Rpa07
not on the reverse side of a cavity wall.
 
  • Like
Reactions: Risteard
Cables in cavities, whatever next. Let the cavity debate begin :rolleyes:
Ok. For THIS application, IF it is a cavity wall, it will be an internal one -between the garage and the hall - so there's no probs with bridging cavity/transference of damp etc.
 
  • Like
Reactions: DPG and Rpa07
brick out behind CU. brick out under upstairs floor. "up and under".
 
On the internally wall clipped direct and capped back entry to the CU.. Approx 30 years ago
If its a rewire, still might think of relocating CU somewhere more accessible, as long as customer willing to pay for new supply distribution circuit IMO
 
Nothing wrong with covering the cables with 3/4mm steel plate.
There is no requirement for the steel plate to be earthed.
Am I being dumb, why won't the plate need earthing?
 
Am I being dumb, why won't the plate need earthing?
read 522.6.101. basically, it' s not an exposed conductive part of the installation.
 
Reg 522.6.204 (iv) mechanical protection.

PS, but the Sunday afternoon DIY'er, won't let a 3mm steel plate stop them from putting up a shelf!
 
  • Like
Reactions: Vortigern
Yeah being dumb was thinking it was earthed protection for cables should someone drill through them but they will/should have rcd protection.
 
You need to ask the purpose of earthing in this particular instance.
No this is an option that does not include RCD protection.
 
Reg 522.6.204 (iv) mechanical protection.

PS, but the Sunday afternoon DIY'er, won't let a 3mm steel plate stop them from putting up a shelf!
Maybe suggest a nice dado rail of this stuff?

IMG_0412.JPG



Sorry, feeling cheeky this arvo ...
 
The simplest answer is to have a 2g socket in the hall and this would create about ,8 inches of safe zone to the ceiling.

Job done
 
Sorry, from the OP's initial post, I thought he was talking about cables supplying the CU.
 
Not sure this can be treated as an internal cavity wall?
It may be that the garage is just a leanto added on to the exterior of the house.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
concealed cables to D.B.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
40

Advert

Thread statistics

Created
jonallcock,
Last reply from
Toneyz,
Replies
40
Views
4,331

Advert