Cables in cavities, whatever next. Let the cavity debate begin :rolleyes:
Ok. For THIS application, IF it is a cavity wall, it will be an internal one -between the garage and the hall - so there's no probs with bridging cavity/transference of damp etc.
Reactions: DPG and Rpa07
brick out behind CU. brick out under upstairs floor. "up and under".
On the internally wall clipped direct and capped back entry to the CU.. Approx 30 years ago
If its a rewire, still might think of relocating CU somewhere more accessible, as long as customer willing to pay for new supply distribution circuit IMO
Nothing wrong with covering the cables with 3/4mm steel plate.
There is no requirement for the steel plate to be earthed.
Am I being dumb, why won't the plate need earthing?
read 522.6.101. basically, it' s not an exposed conductive part of the installation.
Reg 522.6.204 (iv) mechanical protection.
PS, but the Sunday afternoon DIY'er, won't let a 3mm steel plate stop them from putting up a shelf!
Reactions: Vortigern
Yeah being dumb was thinking it was earthed protection for cables should someone drill through them but they will/should have rcd protection.
You need to ask the purpose of earthing in this particular instance.
No this is an option that does not include RCD protection.
Maybe suggest a nice dado rail of this stuff?
Sorry, feeling cheeky this arvo ...
The simplest answer is to have a 2g socket in the hall and this would create about ,8 inches of safe zone to the ceiling.
Job done
Sorry, from the OP's initial post, I thought he was talking about cables supplying the CU.
Not sure this can be treated as an internal cavity wall?
It may be that the garage is just a leanto added on to the exterior of the house.
concealed cables to D.B.
jonallcock,
Toneyz,