Discuss Consumer unit installation in the DIY Electrical Advice area at ElectriciansForums.net

T

TechDave

Hi,

I would like some advice on a new consumer installation if possible. (2 bedroom flat, with kitchen).

Circuit 1, protected with 30mA RCD and 32A MCB: Cooker.
Circuit 2, protected with 30mA RCD and 20A MCB: Ring main, Fridge, Freezer, Washing machine, Combi-boiler.
Circuit 3, protected with 30mA RCD and 20A MCB: Sink canopy lights and shaver socket both located in bathroom.
Circuit 4, protected with 6A MCB: Ceiling lights, bathroom extractor fan.

All RCD and MCB listed are separate for each circuit.
 
Hi,

I would like some advice on a new consumer installation if possible. (2 bedroom flat, with kitchen).

Circuit 1, protected with 30mA RCD and 32A MCB: Cooker.
Circuit 2, protected with 30mA RCD and 20A MCB: Ring main, Fridge, Freezer, Washing machine, Combi-boiler.
Circuit 3, protected with 30mA RCD and 20A MCB: Sink canopy lights and shaver socket both located in bathroom.
Circuit 4, protected with 6A MCB: Ceiling lights, bathroom extractor fan.

All RCD and MCB listed are separate for each circuit.

What about it?
 
Hi,

I would like some advice on a new consumer installation if possible. (2 bedroom flat, with kitchen).

Circuit 1, protected with 30mA RCD and 32A MCB: Cooker.
Circuit 2, protected with 30mA RCD and 20A MCB: Ring main, Fridge, Freezer, Washing machine, Combi-boiler.
Circuit 3, protected with 30mA RCD and 20A MCB: Sink canopy lights and shaver socket both located in bathroom.
Circuit 4, protected with 6A MCB: Ceiling lights, bathroom extractor fan.

All RCD and MCB listed are separate for each circuit.

Hi there TD, what advice would you like? Circuits 1-3, are they protected by a single RCD or are you indicating RCBOs?
 
Last edited:
Hi,

I would like some advice on a new consumer installation if possible. (2 bedroom flat, with kitchen).

Circuit 1, protected with 30mA RCD and 32A MCB: Cooker.
Circuit 2, protected with 30mA RCD and 20A MCB: Ring main, Fridge, Freezer, Washing machine, Combi-boiler.
Circuit 3, protected with 30mA RCD and 20A MCB: Sink canopy lights and shaver socket both located in bathroom.
Circuit 4, protected with 6A MCB: Ceiling lights, bathroom extractor fan.

All RCD and MCB listed are separate for each circuit.


Er, re, why no rcd protection for lights, segregation??
 
I hope he has supplementary bonding in the bathroom without the RCD on circuits serving and passing through.
 
Hi, I would like to hear opinions if this install is correct and sensible.

The circuits each have an individual RCD.

I didn't include RCD on the lighting to avoid nuisance tripping caused by blowing bulbs.
 
Shaver socket on a 20A radial?
Canopy lights on a 20A radial?
A sink in a bathroom?
 
Hi, I would like to hear opinions if this install is correct and sensible.

The circuits each have an individual RCD.

I didn't include RCD on the lighting to avoid nuisance tripping caused by blowing bulbs.


The Trainee section of this forum has a wealth of information!
 
Hi, I would like to hear opinions if this install is correct and sensible.

The circuits each have an individual RCD.

I didn't include RCD on the lighting to avoid nuisance tripping caused by blowing bulbs.

hum.... Not the way to do it.

by seperate rcd do you mean a RCBO?

you need to go back and install a RCBO for the lights.
 
Hi,

I would like some advice on a new consumer installation if possible. (2 bedroom flat, with kitchen).

Circuit 1, protected with 30mA RCD and 32A MCB: Cooker.
Circuit 2, protected with 30mA RCD and 20A MCB: Ring main, Fridge, Freezer, Washing machine, Combi-boiler.
Circuit 3, protected with 30mA RCD and 20A MCB: Sink canopy lights and shaver socket both located in bathroom.
Circuit 4, protected with 6A MCB: Ceiling lights, bathroom extractor fan.

All RCD and MCB listed are separate for each circuit.

TD, I am sorry that I did not read the last line of your post which leaves me more concerned than when I first read it. My earlier questions stand. Are you coming at this from the perspective of an 'enthusiastic amateur' perhaps more akin to DIY? Alternatively, do you have the relevant documents, test equipment and some training and are you therefore looking to be supported in a more professional journey? There is a DIY section that you can request access to and from your question it seems that you are more in the DIY camp. Please give us 'all' the information about your background, your level of skill and equipment and whose property you are proposing working on?
 
Last edited:
Hi, I would like to hear opinions if this install is correct and sensible.

The circuits each have an individual RCD.

I didn't include RCD on the lighting to avoid nuisance tripping caused by blowing bulbs.

Blowing lamps doesn't cause an RCD to trip, it creates a current surge in the normal circuit conductors which can cause an OCPD to operate but not an RCD.
 
Shaver socket on a 20A radial?
Canopy lights on a 20A radial?
A sink in a bathroom?

TD, what have you based your proposal for the rating of your Over Current Protective Devices (OCPDs) upon? How do you propose to place 3 separate RCDs, 1 for each OCPD in a standard consumer unit? In order to define the rating for your OCPDs, you need to be able to understand and apply diversity, particularly for the cooker and Ring Final Corcuit (RFC). The term 'ring main' has not been used for some time in professional circles.
 
The term 'ring main' is still in use today in professional circles with the same meaning it has always had, a distribution circuit in the form of an open ring, usually at 11KV.

It has never been the correct term for a ring final circuit.
 
TD, I am sorry that I did not read the last line of your post which leaves me more concerned than when I first read it. My earlier questions stand. Are you coming at this from the perspective of an 'enthusiastic amateur' perhaps more akin to DIY? Alternatively, do you have the relevant documents, test equipment and some training and are you therefore looking to be supported in a more professional journey? There is a DIY section that you can request access to and from your question it seems that you are more in the DIY camp. Please give us 'all' the information about your background, your level of skill and equipment and whose property you are proposing working on?

Would this extra information help answering my question? If so then I will provide as necessary.
 
The term 'ring main' is still in use today in professional circles with the same meaning it has always had, a distribution circuit in the form of an open ring, usually at 11KV.

It has never been the correct term for a ring final circuit.

d, thanks for the correction ... I had a feeling that it was only ever used by us, the great unwashed ... or uninitiated in the arcane world of electrical distribution and installations. Unfortunately I had not known for sure!

GB
 
d, thanks for the correction ... I had a feeling that it was only ever used by us, the great unwashed ... or uninitiated in the arcane world of electrical distribution and installations. Unfortunately I had not known for sure!

GB

I think it was originally 'ring final sub circuit' but I would have to go and find my copy of the 13th edition to check on that.
 
I think that I may have unwisely chosen to post here, judging by some responses.
 
Would this extra information help answering my question? If so then I will provide as necessary.

TD, answering your question is an incredibly difficult balancing act! More information is required ... but I hope that you have picked up by now the fact that you appear to anyone with some training in the 'field', of electrical installation, to be insufficiently equipped to be doing what you propose to do!
 
I think that I may have unwisely chosen to post here, judging by some responses.

I humbly suggest that you contact one of the moderators for access to the DIY section of the Forum ... Marvo is one of the moderators who was on a little while ago ... PM him or I can on your behalf if you like!
 

Reply to Consumer unit installation in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...
Replies
9
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
712
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock