ketanc

Hello

We have just purchased a new property in Laindon, Essex (SS15) and would like to get the fuse board upgraded and notified to the local authority/certified. We don't yet have the keys to the property, but looking to get an idea for how much this work could cost us in the meantime.

The current board in place is an old rewireable fuse box with 6 ways.

Location wise, if you picture a porch -- on the right hand side is the meter cupboard, tails running upwards through the top of the meter cupboard, disappearing into presumably the ceiling void, above some PVC cladding. Fuse board/gas meter to the left hand side, approximately 3-4m away. Service head cutout reads 60/80A.

Gas meter bonding is in place (will be replaced anyway), water bonding to be done, approximately 12 metres from board to stop cock under the kitchen sink.

I have already bought a new MK 15 way (21 module) dual RCD board (metal enclosure, compliant with Amendment 3) to be fitted, and have a switchfuse that can be used if needed.

Please could you provide a rough quote for the above work - please see attached pictures for further detail.

Please PM me if you would like my telephone number to discuss.

Thanks,

Kay.

P1670697.JPG


P1670483.JPG
 
  • Useful
Reactions: Admin
Thanks for posting this here :)
 
Hi OP, welcome to the forum.

Just looking at those pictures, I think some preliminary work needs to be done before carrying out the CU change. The 'meter tails' looks like to be swa cable, which is incorrectly terminated in the meter box, and the other end at the fuse board, looks like to be a different cable (6181y cable). Might be wrong, difficult to tell looking at some pictures on the web.

Most electricians/companies would carry out some testing & inspection, in any case, before installing a new CU. In your case, it may be prudent to have an Electrical Installation Condition Report carried out, depending on the state of the rest of the installation.

Personally, I would not install a CU purchased by the customer, I prefer to supply & install my own devices & materials, and provide a warranty for them.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Consumer Unit Upgrade - SS15 Essex Area
Prefix
Electrician Jobs 
Forum
Electricians Jobs
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
ketanc,
Last reply from
Midwest,
Replies
2
Views
1,677

Advert