Just doing a Cooker Cable Calculation for a Rangemaster Toldeo 110.
Total Load is 17.4kW
Calculations
17400/230 = 75.65A
First 10A = 10A
30% of remainder (65.65A) = 19.70A
Cooker Point with Socket = 5A
Total Current = 34.70A
Cable will be layed under floor then chased into wall
From my Calculations 10mm T+E should be used.
But.....
The cooker will be used everyday as the customer cooks for work so a high probability that all 4 rings would be on plus oven for hours at a time.
When I calculate all 4 rings being on (4x 2.3kW) (40a)
and the oven 8kw (34.78a)
it totals 74.78A
Over a period of hours surely this would trip the 40a MCB i was planning to install? Is there something I'm overlooking or not quite understanding?
Thanks in advance!