Hi Guys & Gals,

So Im fitting two small 1.7kw storage heaters on Monday. There is already two fitting, fed from an old Wylex cu with rewireable fuses. The cable for the excisting heaters are buried. So my first thought was to fit a new 4 way rcd board so I could add the two new ones. Now I know you can have problems with nuisence tripping of the rcd when the E7 kicks in so, heres what Im going to do!

The customer doesnt want me to chase the walls, he is fine with the cable being run in pvc mini trunking. (not my idea.lol). So I can leave the excisting heaters and board as is. I intend to fit another small 2 way cu next to the excisting E7 cu.

What I want to know is, as both the E7 & 24hr boards are fed from the same service head and meter and they are virtually next to each other, can I use the Ze & PFC reading from the 24hr cu and just make a note on the cert? Or, would you just make a note on the cert why you couldnt carry out the live tests?

Any thoughts or info would be great. If Ive missed something obviouse, I accept your critisism.lol

Jay
 
Is there not then a risk of missing a problem with the tails or earthing conductor (or connections to them) on the Ec7 board? Just asking, like. I notice DNS1 doesn't specifically say use the Zs from the main board. Agreed that PFC is unlikely to be any higher. There is definitely a responsibility to confirm the earthing arrangements and not just take it as being OK.
 
Is there not then a risk of missing a problem with the tails or earthing conductor (or connections to them) on the Ec7 board? Just asking, like. I notice DNS1 doesn't specifically say use the Zs from the main board. Agreed that PFC is unlikely to be any higher. There is definitely a responsibility to confirm the earthing arrangements and not just take it as being OK.

The Zs can be taken by temporarly connecting the E7 cu to the 24hr cu. But I would still need a Ze reading and I think the best way would be at the 24hr cu. I suppose I could always go back at 12am and do the live testing then.lol
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Jay Sparks

Mentor
Arms
~
Joined
Location
Bratford

Thread Information

Title
E7 Ze & PFC measurement??
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Jay Sparks,
Last reply from
MDJ,
Replies
4
Views
1,263

Advert