Chaps, we're installing approx 40 PV panels in Solions (plastic mountings much like the Consoles etc).

We're using an SMA 10000 TL so we need to Earth the array.

When using a TL inverter on standard metal mounted arrays I usually just earth to the mounting rails. Are we going to need to daisy-chain an earth to each and every panel (given that the mounting is plastic)?!

Thanks
 
I don't see that it is needed. The fact that the panels are all seperated means that it would be a pointless exercise. It is safer to keep them seperate and not connect them together in my opinion.
 
Thanks SolarCity.

Just reasoning out loud here, please do criticise! I guess it's the array's mounting system that the DTi guide refers to earthing not the PV panels themselves. The panels are "Class II", double insulated, hence no rqmt to earth them. And the mounting in this instance is plastic so we definitely don't need to earth that. My conclusion: no Earthing required.

This is going on a school roof so if anyone does have any thoughts do let me know!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Earthing Solion / Console mounted arrays
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
DomB,
Last reply from
SolarCity,
Replies
3
Views
1,341

Advert