Just been to an inspection today, as with many of them its suffering from a bit of DIY, bathroom downlights are above 225, so are out of zones, but are not IP rated, so I will probably give them a C3 ? They are double insulated but the earths have been nicely snipped out so are discontinuous & unterminated, so maybe a C2?
I'm still taking far too long with the new forms, is it just me? maybe I'm becoming an old stick in the mud.
 
i thought if they were out of zones they did not have to be IP rated, although prefered.
 
Exactly, but I still think maybe it warrants some mention as these are open GU10s, thats why I was thinking of using a C3
 
You could recommend improvement c3,
But that's your professional opinion. No supporting regulations.

As for the lack of CPC continuity, my code would depend on If it has RCD protection or supplementary bonding to provide protection for bathroom.
 
Think similar question was answered earlier, Just because they are out of the zone does not mean they are suitable for their location.
steam and moisture tends not to know the regs and goes where it likes.
 
  • Like
Reactions: 1 person
The fittings have to be suitable for the environment

In a bathroom I dont believe open lamp downlighters are suitable
Aside from moisture penetration,there is danger of injury should the lamp glass shatter,especialy,if like me the user tramps about barefoot
 
No RCD, but I was going to recommend RCBOs for the lighting circuits anyway. No visible supplimentary bonding, but there is continuity at pipework etc.
 
If theres no earth continuity I would go C2.

BTW I love the new forms, makes it easy to get everything, no more having to remember it all.
 
Hate the EICR's at the moment...filling in one today on NIC software...section F,about 60 odd defects...then when you get to the tick box section you have to reference every one to defects in section F...constantly flicking back and trawling through all the defects....:cuss:
 
Regarding DI fittings, which are becoming more and more prevalent. I struggle between the two options of C2 and C3 mainly because. There is no danger present and there wont be if DA fittings remain, so for it to become dangerous there would need to be a change of fitting to class1 and however fitted it left the earths off, also a C2 tends to lead to an un-satisfactory condition. The problem with C3 is that its worded as a recommendation which i suppose is probably nearer to its actual real danger potential. As its relativly inexpensive to terminate them on a choc block and test continuity and there is some way to explain to the client that it is needed for the future then its easier to justify a C2. I do wish though that the suppliers of these lights create a term position for earth continuity would make life so much easier for DIYers and Electricians
 
Last edited:
the coding would be a code C3 as long as the lights are all class 2 and switches are all on plastic back boxes so plate screws cant become live. But I would make it clear on your test sheet or use addition sheet to clearly explain the dangers would increase if class 2 fittings were changed.

After all you can only report on the installation at its current state.

If you are in doubt ring NIC or ECA techinical (or whoever you pay your money to).
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR codes again earths to double ins fittings
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
andyyoyo,
Last reply from
invisable,
Replies
18
Views
2,932

Advert