Discuss EICR codes again earths to double ins fittings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A
andyyoyo
Just been to an inspection today, as with many of them its suffering from a bit of DIY, bathroom downlights are above 225, so are out of zones, but are not IP rated, so I will probably give them a C3 ? They are double insulated but the earths have been nicely snipped out so are discontinuous & unterminated, so maybe a C2?
I'm still taking far too long with the new forms, is it just me? maybe I'm becoming an old stick in the mud.
You could recommend improvement c3,
But that's your professional opinion. No supporting regulations.
As for the lack of CPC continuity, my code would depend on If it has RCD protection or supplementary bonding to provide protection for bathroom.
The fittings have to be suitable for the environment
In a bathroom I dont believe open lamp downlighters are suitable
Aside from moisture penetration,there is danger of injury should the lamp glass shatter,especialy,if like me the user tramps about barefoot
No RCD, but I was going to recommend RCBOs for the lighting circuits anyway. No visible supplimentary bonding, but there is continuity at pipework etc.
Hate the EICR's at the moment...filling in one today on NIC software...section F,about 60 odd defects...then when you get to the tick box section you have to reference every one to defects in section F...constantly flicking back and trawling through all the defects....:cuss:
Regarding DI fittings, which are becoming more and more prevalent. I struggle between the two options of C2 and C3 mainly because. There is no danger present and there wont be if DA fittings remain, so for it to become dangerous there would need to be a change of fitting to class1 and however fitted it left the earths off, also a C2 tends to lead to an un-satisfactory condition. The problem with C3 is that its worded as a recommendation which i suppose is probably nearer to its actual real danger potential. As its relativly inexpensive to terminate them on a choc block and test continuity and there is some way to explain to the client that it is needed for the future then its easier to justify a C2. I do wish though that the suppliers of these lights create a term position for earth continuity would make life so much easier for DIYers and Electricians
the coding would be a code C3 as long as the lights are all class 2 and switches are all on plastic back boxes so plate screws cant become live. But I would make it clear on your test sheet or use addition sheet to clearly explain the dangers would increase if class 2 fittings were changed.
After all you can only report on the installation at its current state.
If you are in doubt ring NIC or ECA techinical (or whoever you pay your money to).
Reply to EICR codes again earths to double ins fittings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
8K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...