Thanks for the response.
My understanding is that it can also be fitted to a single phase, which I was proposing to do. Apparently it has aa G59 certificate, does this mean that it does not need any additional equipment eg relays?

Looking at the website, the Fronius has a G59/2 certificate and therefore will not need any additional relay. However it is worrying you are asking this question because to fit it you will need to have asked the permission of the DNO and that normally requires that you have submitted the application form with a copy of the relevant certificate already.

Regards
Bruce
 
If it helps we have just had the go ahead for a 5KWp system from Western Power Distribution which reads as follows;

".............at single phase via G59/2 type tested inverters and G83/1 type tested inverters, provided the upper frequency limit of the protection relay is set at 51.5Hz. All other conditions of ENA Engineering Recommendations G59/2 will apply."

I am reading this to say that we don't need an external G59 relay on a G59/2 inverter or a G83/1 inverter (provided we much around with the protection settings). We are looking at an SB 5000TL and based on the comment earlier we will need a password to change those protection settings.

Any opinions/views welcome!
 
Looking at the website, the Fronius has a G59/2 certificate and therefore will not need any additional relay. However it is worrying you are asking this question because to fit it you will need to have asked the permission of the DNO and that normally requires that you have submitted the application form with a copy of the relevant certificate already.

Regards
Bruce
No need to worry as I'm only at very early planning stage!
 

Reply to G59 Relays??? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock