Discuss Generator Voltage Failure in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
12
Tested one of our generators this morning, only about 76KW engine set. Started up fine, took the load of the building fine, connected a load bank, fine. Voltage readings all 240ish, temperature as expected, oil temperature as expected, coolant temperature as expected. 1.5hours later. Chug chug chug. Generator fails. Switches back to mains supply.
Fault on genny is “alternator volts fail”.
My first instinct is failed AVR. Runs genny again off load, readings are 240,241,242v (3phase obviously). So now what? Lol.
Possibly a faulty alternator? Is it worth checking the stator winding? I’m electrically biased and my mechanical knowledge is basic I’ll prewarn you. Thanks in advance.
 
Does the standby set have any bushes that may be worn down to far and not making contact on the alternator slip rings?
 
mate, its saturday get yourself down the beer garden and worry about this on monday
LOL, it's POETS day, you have started early
 
Like I have said hundreds of times here, the Jocks are constantly pi$$ed lol, say no more pmsl
 
‘Chug chug chug’ to me suggests that maybe the engine has an issue maybe fuel filter or the water separator hasn’t been emptied in a while.
Ah yes Dave, couldn't really be electrical, if the Prime mover is playing up, fuel problems, injectors blocked, filter blocked, over heating, needs a diesel Mechanic to have a butcher I would think.
 
Sounds like a engine side failure. Because of the alternater fault I would check all the electrical connections related to it. If it is a stand by set I’m guessing the trickle charge set up will replenish the battery’s and perhaps hide the altonator fault if it’s only ran for short periods
 
Sounds like a engine side failure. Because of the alternater fault I would check all the electrical connections related to it. If it is a stand by set I’m guessing the trickle charge set up will replenish the battery’s and perhaps hide the altonator fault if it’s only ran for short periods
Yes mate it’s a standby set. 24v starter battery which is charged via a 24v rectifier (from the engine control cab).
I see what you’re saying though.
 
Ah yes Dave, couldn't really be electrical, if the Prime mover is playing up, fuel problems, injectors blocked, filter blocked, over heating, needs a diesel Mechanic to have a butcher I would think.
I think that’s a good idea checking the fuel filters etc. It’s in a remote area and probably runs for around 4-5 hours a year, if that
 
Customer of mine decided to go green and buy bio-diesel for their standby generators. Trouble is the stuff doesn’t keep and turns to some sort of sludge. They came to test run some of the sets and they all cut out after a few minutes. They then had to spend a fortune replacing filters and cleaning out injectors then having the tanks pumped out and cleaned prior to refilling with proper diesel!
 
Customer of mine decided to go green and buy bio-diesel for their standby generators. Trouble is the stuff doesn’t keep and turns to some sort of sludge. They came to test run some of the sets and they all cut out after a few minutes. They then had to spend a fortune replacing filters and cleaning out injectors then having the tanks pumped out and cleaned prior to refilling with proper diesel!

proper diesel aint what it used to be now its ultra low sulphur and can suffer the same enzyme sludge as the biofuels
 
There's a regulator on a heatsink which has worn out, new one is about £30 this powers the Pcb which has the exciter driver that does the output regulating when the load goes up, you'll see the module screwed onto the engine body where the heat from the engine knackers it.. You can get one online, they are rivited shut and disposable
 
Do the S/BY set have any kind of fault diagnoses charts you could look at? these thing are so well built and tested it could be something very simple, please leet us know the outcome.
 
Customer of mine decided to go green and buy bio-diesel for their standby generators. Trouble is the stuff doesn’t keep and turns to some sort of sludge. They came to test run some of the sets and they all cut out after a few minutes. They then had to spend a fortune replacing filters and cleaning out injectors then having the tanks pumped out and cleaned prior to refilling with proper diesel!
There used to be a few people near me that made bio diesel for themselves and had bought all the machinery and chemicals to add into it, they got a visit from the customs and tax and that was the end of that, no more collecting chippy veg oil.
Now refineries are adding veg and ethanol in and your car diesel and petrol are duff, the fuel you buy can void your warranty as the chemistry doesn't match the manufacturers benchmark for fuel.
 

Reply to Generator Voltage Failure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello community, first time post.... I'm currently working on a bathroom renovation, in which I'm installing a 9kW steam generator/boiler. I'm a...
Replies
10
Views
5K
Hi folks I am retired and only tend to read the weekly summaries. I read the long-winded thread re. the storage heater and MCB tripping (thread...
Replies
14
Views
2K
Hi all, hoping someone can offer some knowledge/experience of immersion heater fault finding. My parents-in-law's imersion heater stopped...
Replies
23
Views
7K
I
This posting may be of interest to anyone continuing to use Enecsys micro inverters: The Enecsys micro inverters use a DC to DC boost...
Replies
2
Views
4K
L
Hi lads, in most of the installations I would be involved with, we have diesel generators suppling all our equipment. In one particular station it...
Replies
14
Views
3K
Lighthouse Phil
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock