Bernard1991

hi i have a thread under noisy contactor and said i would put annother thread up relating to a side subject from that thread

(please do not reply untill this part in the brackets is deleted just got the original design up for now not got enough time to show the changes that will be made from the knowlege i learnt in my previous thread shall get the second part of up tomorrow then remove this section in brackets many thanks bernie)
 
original system (scrapped looking for new ideas)

** Ignore this bit the idea has been scrapped I'm looking for new ideas, toward the end of the thread (page2) **

note: not in operation genny has not been connect nor will be conneted untill everything is complete
the genny has a output of 6.5kva

here is the original version i first put together
1) its a two contactor system both n/o
2) each contactor has its own control relay (2a 250v contact double pole, 12v dc coil with internal diode)
3) the main change over relay is a double pole double throw (two way) and the n/c connection (when the relay is dead) goes to the mains contactor control relay and the coil (230v) is energised when the genney is powered up and switched on at the main unit (switch is 250v rated) thus turning off the relay controling the mains contactor and energising the genny contactor control relay then engageing the contactor
4) both contactors has its own lumination on the main unit to tell the user if its engaged
5) the main unit has a lumination to tell the internal dc transformer is working
6) volt and amp meter telles user how much current is being used and the voltage out put (so i can work out how much power is being used and how much surplus there is)
7) everything is fused to protect the circuit
8) start and stop button for remote start and stop (when the genny has a auto choke and starter motor installed)

images below:

IMG_1588.jpg
IMG_1593.jpg
IMG_1596.jpg
 
Last edited by a moderator:
Well there is no way you can provide a mechanical interlock on what you have there!!

If you're determined to include a Generator into your mains system, then be wise and purchase a made for purpose Transfer/changeover switch either manually operated or automatic...

What is the make/model of the generator you intend to use for this installation, and does it incorporate a decent AVR on the alternators output??
 
  • Like
Reactions: 1 person
Hi engineer I am totally re designing the part of the system with the contactors I shall be changing them to the same make moving both into the same box and having a interlock between them I asked in the first post if everyone could hold off a reply till I got the second half on only wanted to show the changes from what I had to what I will have from what I've been told and advised on what I got now is being scrapped (least the contactors in two places) shall have the other section on tomorrow not got enough time now as I'm in work at 8:15
shall also get the exact model number off the genny after work it's buried in the shed at this moment in time
 
You may want to consider two timers in the control circuit of the contactors, this will stop the "chatter" problem alluded to by Lucien in the other thread.

The contactors will have to be physically side by side to fit the mechanical interlock between them
 
As much as I admire spirited thinking and creativity...... are we simply not just reinventing the wheel, here? An off the shelf changeover unit would be much quicker and cheaper?!
 
  • Like
Reactions: 2 people
They will be side by side mate the armoured cable going to the shed is a 6mm 4core (not ideall would rarther have two cables but it's only temp till the shed is re built in the near future)
how ever I have found a good price changer over switch on eBay (£60 with a clad box) only concern I have with a switch is it's inaccessible where the house c/u is I'll have my mother call me every time the power goes out and why there's no power when the genny is running and not something I want if I'm ever fault finding a pain in the back side break in a ring main but if the new version I have in mind is still a big concern I'll just scrap the lot and go with a change over switch and ignore any calls from my mother when at work
 
As much as I admire spirited thinking and creativity...... are we simply not just reinventing the wheel, here? An off the shelf changeover unit would be much quicker and cheaper?!

possibly if you know to a place that has them for less than £100 so far I spent less than that (£50 I can get back just wacking the contactors I got on eBay as for the relays I'm allways dabbling with electronic circuits so will find some other use for them)
 
IME buying off the shelf ATS works out cheaper for the smaller sizes, and will be compliant, making your own does work out cheaper for the larger sizes or custom built ones sometimes, but building your own needs properly testing and certifying, I have done both.
 
Just had a look on rs components and found out there's 4pole contactors with two n/o and two n/c poles

if I can get a 63a 4pole 2n/c and 2n/o (our main fuse is 60a) contactor would it be better and be safer and also have a delay on it to allow the genny time to fully spin up

so say have the genny on the n/o side and the mains on the n/c side start the genny when there's a power cut after 3 seconds or more the contactor will energise and isolate the mains and connect the genny to the house

whats you views on this guys?
 
Please do not try to do this on the cheap, no disrespect meant, but you are clearly out of your depth.
Either buy a proper bespoke system, or forget it.

There are implications that you have not thought of, and attempting to do what you are trying to achieve will likely end in tears.

The internet is no way to try to learn what you are trying to do.

This is the best advice I can give you.
Sorry I am out.
 
I'm not trying to do it on the cheap if I wanted to do it on the cheap I would have got a £60 basics changeover switch in a metal clad box but though my mum knows 0 about electrics so would be better if all she had to do is turn the generator on and not have to climb on chairs just to flick the switch to change it over she isn't getting any younger neither is my dad and I won't be living at home forever so I come on here to learn about generator installations and work out the best course without it costing a arm and a leg

at least I sought advice before going any further I knew a guy who had a length of flex with two plug tops one either end he pluged into his genny and the other into a socket then he would turn the main switch off on the c/u then start up the genny now surely you cannot get any more dangerous than that no Rcd protection and no fool proof isolation
 
I'm not trying to do it on the cheap if I wanted to do it on the cheap I would have got a £60 basics changeover switch in a metal clad box but though my mum knows 0 about electrics so would be better if all she had to do is turn the generator on and not have to climb on chairs just to flick the switch to change it over she isn't getting any younger neither is my dad and I won't be living at home forever so I come on here to learn about generator installations and work out the best course without it costing a arm and a leg

at least I sought advice before going any further I knew a guy who had a length of flex with two plug tops one either end he pluged into his genny and the other into a socket then he would turn the main switch off on the c/u then start up the genny now surely you cannot get any more dangerous than that no Rcd protection and no fool proof isolation


Please don't tell me you are serious?

The courses have a cost for a reason, not to deter you from doing them but because of the effort and time people have put in learning about them so it can be done safely.

That statement makes a Electrical Trainee sound lime they know what they are doing.
 
To the OP
Cost cannot be the main and overriding concern where safety of the user and others is put at risk for the sake of a few pounds this coupled with the distinct lack of knowledge you possess regarding generator switching is a recipe for disaster

Your best option is forget it or spend some cash and get someone in who knows what they are doing
 
Well I'm just going to scrap the lot and go back to basics (no pun intended)
below is a picture of a basics changeover switch generator transfer 125a single phase metal clad m125cs (that's how it's advertised) will that be ok?
And later ill put the model number of the generator I have and ask if that's ok to use
 

Attachments

  • image.jpg
    image.jpg
    91.6 KB · Views: 110
Hi,

Surely you can get hold of an Automatic Change-Over switch, then your parents can sit back in comfort and let the little magic box do its business.

Regards.
 
I can see a number of worrying things there. But let's start with that connector marked 'hook up to genny'. Am I going blind or is that a socket-outlet? Please correct me if I am not seeing it for what it is...

And another thing that's actually more dangerous, do I see the tops of the contactors accessible from outside the enclosures, so anybody could (intentionally or accidentally) press the manual operation button and cross-connect the two sources?

Perhaps I had better not look any more...
 
I can see a number of worrying things there. But let's start with that connector marked 'hook up to genny'. Am I going blind or is that a socket-outlet? Please correct me if I am not seeing it for what it is...

And another thing that's actually more dangerous, do I see the tops of the contactors accessible from outside the enclosures, so anybody could (intentionally or accidentally) press the manual operation button and cross-connect the two sources?

Perhaps I had better not look any more...

It's a 32 amp three pin socket (like on a caravan)
but I have scrapped the idea now so it's redundant and will be removed
 
So you had a plug connected to a source of energy. With apologies for the pun, I recommend you pull the plug on this project and have a commercial transfer switch fitted. It really isn't worth the (many) risks you are taking with the present setup, due to lack of familiarity with the requirements.
 
I have scrapped it and shall put the contactors used on eBay to get my money back
The immage I put on post 16 would that be safe to use for what I intend in terms of a manual change over
and shall like said in other posts look into a proper pre build control unit as a second option and get a good wiring diagram wire it up myself following it and get it properly commissioned and even have the commissioners number to hand if I get stuck (should be fine with a wiring diagram first year college I was drawing them up and in electronics I was making timer circuits and led light circuits all for 12v dc use and not ever supplied by 230v power)

But all this hinges on the generator and here's some info on it
couldn't get it all it's seriously buried under who knows what

aulternator
type. Mr1180 j609b
code. 0330202235
Date. 1999

output:
50hz
56a 110v
26a 230v

engine rpm 3000
made by. Vanguard
if there's anything more in particular anyone needs to know off the alternator let me know and I'll see if I can find it
 
last thing I need is to be pulled into a can of worms here...
I work with auto change over gents on a almost daily basis... Buy a Mains Fail change over contactor unit off the shelf,, it will have all the wiring already done and will include a mechanical interlock too.
By the sound of the description of your genny, I don't think I will have a decent AVR, so don't supply any sensitive electronics with it...
Have you thought about Earthing of the genny ?? It will need its own earth rod / matt and neutral and earth linked in the alternator
The list could continue....
 
  • Like
Reactions: 3 people
Hi Phil I had a feeling I would have to do something with re guards to earthing other than just it's supplied earth
I did think on the lines of a earth rod in the ground connecting to the neutral like you said I presumed this as when I was studying electrical they told us a bit about transformers on the grid and the earth was linked to the neutral and rodded to ground, won't go into it too much as we all know why it's done that way (different kettle of fish a transformer from a genny I know)

ill see if I can find a wiring diagram for the genny but on top of alternator there's a box with two 110v plugs and two 230v plugs with thermal cut outs built in for both voltages and a switch on the front to change it from 110 to 230 and all the cables come out of the alternator into it

as for the changing over from mains to genny my dad wants it to be manual (to quote him simplicity is efficient) so a few posts back I put a picture of a basics generator change over switch will that be good to use or would you recogmend something else that would be better suited?

As for the AVR I'll see if I can find one for my genny
And the only electronics we have is the useuall house hold items tv, sky, computers, router, iphone, iPad and drivers for led down lights if you want to count them
 
And the only electronics we have is the useuall house hold items tv, sky, computers, router, iphone, iPad and drivers for led down lights if you want to count them

All of which can be blown/damaged by a genny without a decent AVR of one kind or another...

An ATS can also be used in manual operation, and to be honest, if this gen-set/transfer switch is not going to be located in an easily accessible location, then ATS operation makes much more sense than manual operation. Especially if it means going outside in the pouring rain etc, to switch the damn thing on or off!!
 
Contactor buzzing! we have either saved your day or shown you the path to a nightmare ....either way i hope you can now appreciate why you were initially been given a rough ride ..... i hope by now you can appreciate with the wiring plan you originally supplied you were way off mark and in for a steep learning curve .... given both the threads there are still areas we haven't even mentioned ... im thinking you dont really get it that you can't design a compliant system by forum shopping and picking it up bit by bit....

A little knowledge is your enemy here and just wish you would appreciate the regulations and standards you need to comply to; some life critical others down to simple things like correct panel design etc (ot so critical).... no offense but you could be several yrs off the knowledge required to get this right.
 
  • Like
Reactions: 1 person
Your man has been dribbling on about automatic Gen changeover so his wrinklinly old mother doesn't have to stand on a chair to turn a switch.
She's still going to have to leg it down the the shed in dark to turn the damned thing on.


OP, I think you'll find your parent(s) can manage quite well without you! :-)
 
  • Like
Reactions: 1 person
She's still going to have to leg it down the the shed in dark to turn the damned thing on.

Or top up the fuel or is that the next automated project
 
Was them last three posts (#27, #29, #30) realy neciccerry I don't mind a little criticism but taking the Micky is uncalled for ok I may have been wrong about something and I admit it that's what these forums are for to double check these thins
but it doesn't give anyone the right to take wet it's immature understandable if you knew me and I was a complete ----er but you don't know me and I'm not

getting back to to the subject I want to get this sorted and get it done so it's safe either way I'll have a certified guy check it over and to get advice from

as as for starting the genny my dad can install a proper starter and auto choke to it (he used to work on the engines that power small gennys, mowers and other garden equipment he's a old school mechanic)
then I can put together a little unit in the house with a start and stop key or button or combination of the two and the fuel tank is simpler just find a tank with a larger capacity and install it where the genny will be permanently fixed
then have a manual change over switch, all that if I choose to not use a completely automatic system
so I shall have a look on that site that Geordie spark gave me
 
Used Generators for Sale by FW Power - New and Used Diesel Generator Supplier

OP, take a look at the Lister engine / alternator for sale here. Its a Lister HR2, a work horse of an engine, coupled with a decent alternator., but the control cabinet has a new 'Deep Sea Unit' as its brains,, these units can be programmed to do so much and give so much info about the state of the engine. All new cabinets that are being installed on Irish Lighthouses use these Deep Sea units.
 
Hope you have thought about the noise aspect of the gen because I have lived on a gen power army base lol. And the noise is intense even in a well designed gen pad lol

Have you also found out why the prime power is so un- reliant also? Is it location?

Who is the DNO?
 
Hi timbobelfast
if I read your questions correctly I'm not sure why our main supply from our dno (westernpower) sometimes cuts out, it's more reliable than it was, it used to allways go out when the weather changed but now it's random last time was dude to maintenance of the lines and the transformer for my area is in a near by field (we live out I the country side nearest town is two miles)
the reliability of our mains is good just handy to have a back up incase the power is off for a long period and with news reports of planned black outs in 2014/2015 we will be the first to be turned off
heard reports that they won't be so bad (say the government) but I don't believe it by a long shot but let's not drift to polotics allways end in arguments lol

and if your last question was to see if I know who they are there the company who own the power network and operate it

I used to install solar electric systems for a company (I just put inverter up and connected everything up tested and switched it all on) and they had to inform the dno for that area about the install amongst other things I wasn't involved in the office I was just the installer and the office signed it all off from the test results I sent them then after they told me the readings where acceptable I then done the big turn on (but that's annother subject and won't go into it too much)

as for noise I know some can make be quite loud so It would have to be shut down after a certain time of night
 
Last edited by a moderator:
Was them last three posts (#27, #29, #30) realy neciccerry I don't mind a little criticism but taking the Micky is uncalled for ok I may have been wrong about something and I admit it that's what these forums are for to double check these thins
but it doesn't give anyone the right to take wet it's immature understandable if you knew me and I was a complete ----er but you don't know me and I'm not

getting back to to the subject I want to get this sorted and get it done so it's safe either way I'll have a certified guy check it over and to get advice from

as as for starting the genny my dad can install a proper starter and auto choke to it (he used to work on the engines that power small gennys, mowers and other garden equipment he's a old school mechanic)
then I can put together a little unit in the house with a start and stop key or button or combination of the two and the fuel tank is simpler just find a tank with a larger capacity and install it where the genny will be permanently fixed
then have a manual change over switch, all that if I choose to not use a completely automatic system
so I shall have a look on that site that Geordie spark gave me

In your first paragraph you summed yourself up perfectly if you take life to seriously I don't recommend posting anything on a forum

re post #29 You seem to have over looked a lot of things so I was just making sure you had addressed the fuel supply

I assume you are aware of the fuel storage regulations for your larger tank or is that just another minor technical problem to sort

This whole thing to me appears to a very expensive solution to provide a small amount of power as the generator would need to be run regularly to prevent engine and fuel system problems and then you have the problem of the fuel in the tank going stale before it is used as well

You might actually be better with a battery bank and an inverter
 
Used Generators for Sale by FW Power - New and Used Diesel Generator Supplier

OP, take a look at the Lister engine / alternator for sale here. Its a Lister HR2, a work horse of an engine, coupled with a decent alternator., but the control cabinet has a new 'Deep Sea Unit' as its brains,, these units can be programmed to do so much and give so much info about the state of the engine. All new cabinets that are being installed on Irish Lighthouses use these Deep Sea units.

Is that Lister HR2 engine 2 stroke or 4 stroke??
 
You might actually be better with a battery bank and an inverter

Battery storage for any decent capacity or length of time via an inverter, is going to be far more expensive, in both the short and long term of the system than a standby genset.
Hazard a guess of the cost of batteries that can supply say a 5kw load for 3 hours through a suitably sized/rated inverter??

No idea about petrol fueled engines, as i've never used them, but you shouldn't have much if any of a problem with modern diesel fuels. Nothing stopping you running the system for 15 minutes or so say every month, to keep the all the moving parts of the engine lubricated.
 
2 stroke or 4 stroke
The HR series are aircooled 4-stroke D/I diesels of about 1000cc P/C, widely used for construction plant, gensets, pumps, marine aux. duty & small inland craft propulsion. Also made in watercooled form as the HRW. Long time since I had one of those apart!
 
Lister will be diesel, lovely things.

One thing about large fuel tanks, both diesel and petrol go “sour” after six months or so due to evaporation and settlement.

To keep the engine in condition it needs to be run on load regularly. Otherwise it cokes up. I’ll guarantee it fails when you need it!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
genny system
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
62

Advert

Thread statistics

Created
Bernard1991,
Last reply from
Lighthouse Phil,
Replies
62
Views
7,358

Advert