Hi guys, been doing more testing and reporting on small blocks of flats and came across this scenario.

Block is PME with a small intake at the bottom containing most of the meters. The sub-mains/laterals then run through pvc conduit to the ccus in the flats where there is an Henly block making the PME connection. I think this is wrong as any fault current would have to go through the meter. What's your thoughts?
Pix below...


IMG_6179.JPG IMG_6181.JPG IMG_6183.JPG
 
totally wrong. the PME connection N-E must be made at the cut-out, before the meters. definitely a C2 at best.
 
but where is the main earthing conductor for each flat connected to N?
 
If I've understood the installation correctly, it's prohibited by reg 543.4.1 and ESQC reg 8(4) is quoted also.

The PME connection is only just in the flat each time, before the Neutral goes into the ccu, it was because the meters are remote it means a fault current would go through the meter.
Some of the flats have had the meters moved into them, (that's the Henly blocks you can see above the trunking in my original post) and the pme connection is before meter so I have no issues with them.
 
Ok, but where is the supplier's fuse? ( i.e. Can you describe the fusing arrangement for the building and the flats :) )

Yes the service head is a 100A 3 phase PME job that feeds a Ryefield board. Each fuse feeds a flat. Some of the meters for the flats are mounted on a trunking next to the Ryefield board. As said the laterals are run in PVC conduit with no separate Earthing conductor.
 
Sounds like the PME is done ok at the building cut out, but they have failed to link the MET to each of the flats. Instead they have created additional N-E links in contravention of reg 543.4.3 (is my thought).
 
Essentially what you have there are PEN/CNE conductors within the installation. Presumably this is within the BNO network, although without DNO authorisation there is almost certainly a breach of ESQCR there.
 

Reply to I think this is wrong, thoughts please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
1K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K
Hi everyone, hope you’re all doing well. Got a job starting next week for a rewire of a studio flat, currently they have 10 mm T&E as metre tails...
Replies
9
Views
7K
Hi All So i have just got a job of doing a rewire on a small flat, which includes change of DB etc... Currently this is fed from a 3 phase DB in...
Replies
8
Views
899
Hi Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock