The multimeter function you could also find on the low ohms function of your MFT and or standalone megger. What is the resistance of the fault?
Discuss Locating distance of earth fault in buried swa in the UK Electrical Forum area at ElectriciansForums.net
What is the resistance of the fault?
Update
Had a good go at it today in more of a structured manner has other visits were just quick afternoon visits.
Took all lamps ( led) out and all connectors off cabling leaving just cables to test.
40 Mohm with 500v insulation tester L-E N-E.so cable OK.
Went to each fitting and added connectors and lampholders testing each time.as I added lampholder resistance go lower.
Reading with no lamps in 11Mohm.
Connected back up to supply and RCD held.
Has I started putting led lamps in I noticed about 17 of the lamps had about half the individual LEDs lit.
Could a combination of all these have been the problem.
Left with 15 drive lights and 3 wall fittings working fine.new lamps been ordered.
What have I learnt?
Work in a structured manner when fault finding rather than dipping in and out not achieving much other than confusion.
Thanks for everyone's comments on this issue a great help