short story, I've come across a 3 phase distribution circuit wired in 4mm singles on 63a hrc fuses. I found this because 1 of the phases was on a 20a and had blown. this seams wrong to me but as I said I don't have much ind experience. this is a new circuit from a tap off box. also I don't want to drop someone in the rubbish if it is wrong.
 
So one phase was 20A and the others 63A? If they are pvc singles contained in conduit they are only rated at 28A. If they are thermosetting (BS7211) they are rated at 44A.
 
Who would you be dropping in the crap that so concerns you and why do you priorities this against both public and property safety?

My next concern is you are getting involved with situations you have little to no experience in, it may be the fact that overload protection of the cables is not afforded due to an exemption found in the BS7671 regarding fixed load equipment, this could be what you have come across although it's also common to find bodged work and poor design so with knowing all the details of electrical install and the load itself it's hard to call on whether it complies or not and if it's a hazard.
 
the person I don't want to drop in it, is who ever connected the 4mm to the 63a fuse. the omission of overload protection was what I was thinking of but as a distribution circuit I can't see how that would apply (my lack of experience). the 3 lives have been clamped and read 17, 15 and 26a respectively. this is not my problem to fix but I feel I should raise my concerns if they are justified.
 
What is it supplying, it is not just overcurrent protection but the issue of the conductors withstanding fault current.
 
So it supplies a dist board.
 
Those conductors are undersized, with a dist board there is no way of knowing any future loading, but if alterations/additions are carried out hopefully a competent person SHOULD see the situation. Theoretically there is a possibility that with any future loading those conductors could seriously be overloaded.
 
Are you saying the fuses in the tap off box are 63a or the the main bus bar trunking?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
my industrial inexperience?
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Adie moore,
Last reply from
Adie moore,
Replies
11
Views
2,205

Advert