Been on a job today and debating what to put on the certificate.

The DNO in early 2013 upgraded the supply and installed PME. The previous setup had an earth rod installed. This is still connected to the main earth terminal. Not sure what type the previous set up was as the customer is none the wiser, As the upgrade was done just before she bought the house.all she cared about was that things come on and turn off when required.

I am only filling in a minor works certificate as it only involved extending a radial.

In terms of earthing arrangement would you all agree i have been okay to record it as PME with a supplementary TT rod. making a note in the comments box mentioning there is a rod aswell? Guess it will be 18th edition compliant before its time!

I have so far filled it in as a PME system and am wondering if in addition to recording the Ze of 0.29 ohms i should record Ra aswell? I haven't measured it as of yet as i went with its a PME with supplementary rod.

I have to go back Monday next week to change a light fitting, so can measure Ra if needed.

It does raise the prospect of whether the certificate forms will be updated to reflect 18th edition if supplementary rods are going to be needed.

Thoughts welcome as it is something I haven't dealt with or potentially noticed before as most of my experience is light commercial such as pubs.
 
If it's been changed to pme then why bother with the earth rod?
By definition from the DNO having Carried out works it's a TN-CS earthing arrangement
 
  • Agree
Reactions: Davisonp
i'd just do as you suggest. record Ze and PME earthing , with a note saying there is a supplementary rod.
 
  • Agree
Reactions: DPG and Davisonp
or diss the rod and say nowt.
 
  • Like
Reactions: Rpa07
or diss the rod and say nowt.
Did think of that, but given the way people get slaughtered if something goes wrong this day and age, i figured its best to play it by the rules and not conceal things. ALso given the potential changes regarding supplementary rods in the 18th ed its worth thinking about now.
 
I imagine the younger people reading would see @Pete999s' comment "Diss the rod" as
That is a crap rod and looks bad innit, nowadays:cool:
i know me and pete are both old coffin dodgers, but surely you can tell us apart. i'm the good looking one. :p:p:p
 
It's TN-C-S. The fact it also has an Earth rod is irrelevant (in fact, it is a very good thing). No need to worry about Ra of the rod.

Most of the rest of the world requires Earth electrodes on TN-C-S installations - it's about time JPEL/64 caught up.
 
  • Agree
Reactions: sparkie141
Basically they put a list of new regulations into a hat, give it a shuffle and each member picks out a regulation and they have a good chuckle over it!
Let the b*stards (that's us)figure this one out mhaaaaahhhaaa
 
Look in the front of BS7671 you will see the listings for the brains trust.
Ah okay, didnt get that on the find the correct answer test/ wordsearch for grown ups that is the 17th ed.

It sounds like the same method american psychiatrists use when they update the DSM book of mental disorders. basically a shrink proposes a new condition based on what he has seen in patients or hospital. if enough other shrinks agree and put there hands up it ends up the big book and people can be labelled as having the said new condition. absolutely bonkers... and that's just the shrinks.
 
  • Agree
Reactions: Rpa07
Basically they put a list of new regulations into a hat, give it a shuffle and each member picks out a regulation and they have a good chuckle over it!
Let the b*stards (that's us)figure this one out mhaaaaahhhaaa
Careful now some forum members maybe offended by that :tired:
 
How old is this thread?
Don't you all know the proposals put forward for next year 's edition of BS7671?
 
QUOTE="Gavin John Hyde, post: 1290550, member: 101583"]JPEL/64 ????
Whats that when its translated in to English?[/QUOTE]
probably a earth planted potato or could be IEE joint chiefs of staffs
 
  • Like
Reactions: DPG and Wilko
I'm trying to think of something funny to say about all the new books etc I'll have to buy
yeah like the beano or dandy !
 
  • Like
Reactions: Wilko
....Most of the rest of the world requires Earth electrodes on TN-C-S installations - it's about time JPEL/64 caught up.
We were a proud nation of Engineers ,
(I'll blame global warming making us all equal)
 
  • Funny
Reactions: Rpa07
We were a proud nation of Engineers ,
(I'll blame global warming making us all equal)
is that boiling the kettle at the same time!
 
  • Like
Reactions: static zap
Why can't they simply defer the 18th until 2020 ?

Save us all a lot of money....
Need to keep the printing industry alive , more regulations , Brexit red tape ..!
 
Too many mirrors David.

This reminds me of a house I moved in to in 1975 built in 1936. After a few years I decided to check the earth out as I noticed we had 2 overhead wires + and -. There was no earth system at all so I
Bought an earth rod and wired it to the fuse box accordingly.
Then the MEB came and wired the earth to neutral WTF. If that had never been brought in would they allow that now?
I think they also used to use a 12" square galvanized plate buried in the ground. I've just dug one up here, house built in 1934.
 
Too many mirrors David.

This reminds me of a house I moved in to in 1975 built in 1936. After a few years I decided to check the earth out as I noticed we had 2 overhead wires + and -. There was no earth system at all so I
Bought an earth rod and wired it to the fuse box accordingly.
Then the MEB came and wired the earth to neutral WTF. If that had never been brought in would they allow that now?
I think they also used to use a 12" square galvanized plate buried in the ground. I've just dug one up here, house built in 1934.
 
  • Like
Reactions: Rpa07
Too many mirrors David.

This reminds me of a house I moved in to in 1975 built in 1936. After a few years I decided to check the earth out as I noticed we had 2 overhead wires + and -. There was no earth system at all so I
Bought an earth rod and wired it to the fuse box accordingly.
Then the MEB came and wired the earth to neutral WTF. If that had never been brought in would they allow that now?
I think they also used to use a 12" square galvanized plate buried in the ground. I've just dug one up here, house built in 1934.
 
Too many mirrors David.

This reminds me of a house I moved in to in 1975 built in 1936. After a few years I decided to check the earth out as I noticed we had 2 overhead wires + and -. There was no earth system at all so I
Bought an earth rod and wired it to the fuse box accordingly.
Then the MEB came and wired the earth to neutral WTF. If that had never been brought in would they allow that now?
I think they also used to use a 12" square galvanized plate buried in the ground. I've just dug one up here, house built in 1934.
 
and this week's prize for the most duplicate posts goes to..................................................................................................................................................................................................

the rabbit.
 
So was that 4 earth rods?
 
  • Funny
Reactions: David M
Let’s open an old thread.

looking fo4 a brief answer. Wishful thinking.

on a pme system having an earth rod as an addition is perfectly ok in my opinion.


im working for and under a new electrician at work.
we have had a distribution board fitted by outside contractors. They have earthed via a 16 mm earth conductor within the 3 phase SWA supplied from a PME system. They have also popped an earth rod in at the new distribution board. We are going to run feeds of this board for various stuff.

the new electrician wants to convert to TT or get rid of the earth rod As he thinks it’s wrong because of “potential differences” I disagree.

Am I wrong? I’m willing to accept this If I am,

but I know earth rods where proposed as additions in PME in the 18th. So I’m sure it’s OK.
 
Let’s open an old thread.

looking fo4 a brief answer. Wishful thinking.

on a pme system having an earth rod as an addition is perfectly ok in my opinion.


im working for and under a new electrician at work.
we have had a distribution board fitted by outside contractors. They have earthed via a 16 mm earth conductor within the 3 phase SWA supplied from a PME system. They have also popped an earth rod in at the new distribution board. We are going to run feeds of this board for various stuff.

the new electrician wants to convert to TT or get rid of the earth rod As he thinks it’s wrong because of “potential differences” I disagree.

Am I wrong? I’m willing to accept this If I am,

but I know earth rods where proposed as additions in PME in the 18th. So I’m sure it’s OK.

If the rod is bonded to the distribution board earth then surely there can be no potential difference. Did he mention which two points he was thinking of the difference being across?

I agree with you and really can't see the problem here, but it will be interesting to hear other views.
 
  • Like
Reactions: Deleted account
If the rod is bonded to the distribution board earth then surely there can be no potential difference. Did he mention which two points he was thinking of the difference being across?

I agree with you and really can't see the problem here, but it will be interesting to hear other views.
Thanks for quick responce. My thoughts exactly. Just had to check in case I had got it wrong.


This new guy has much more experience with these types of systems than me or so he said at interview, coming from industrial and comercail instals, but I’m starting to suspect he’s been relying on others to design his jobs.
 
Thanks for quick responce. My thoughts exactly. Just had to check in case I had got it wrong.


This new guy has much more experience with these types of systems than me or so he said at interview, coming from industrial and comercail instals, but I’m starting to suspect he’s been relying on others to design his jobs.

To be honest I'm no expert either.

Be interesting seeing what else he says.
 
  • Like
Reactions: Deleted account

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Gavin John Hyde

Esteemed
Arms
Patron
~
Joined
Location
Somerset
Website
http://www.sulis-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Sulis Electrical Services Ltd

Thread Information

Title
PME system with earth rod aswell
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
49

Advert

Thread statistics

Created
Gavin John Hyde,
Last reply from
timhoward,
Replies
49
Views
19,686

Advert