ayjay
well, at least she can hang her washing out to dry on the pipe, nothing too heavy mind
just smalls
-
just smalls
-
Discuss Surely there must be a Reg against this?! in the UK Electrical Forum area at ElectriciansForums.net
Nothing extranious in the the garage but surely if there was I could use the armour as an earth?.
Well maybe...maybe not....if you use 6.0mm 3c XPLE SWA the sheath has a copper equivalent of 7.39mm....not big enough for a 10mm main bond if the supply is TNCS.....
Yeh someone just said that. If needed I'll just run the seperate 10mm. I never knew until this thread that the armour was 7 odd mill though, learn something new every day!If you use 3c6mm you will have 6mil cpc + 7 odd mil for the armouring!
If you want for the regs on that conduit, look for conduit support spacings, looks like you have about 2 m run with no supports(no compliant), then white pvc is not good in sunlight(not sure about regs on this one), and then I see this conduit being a good support for some numpty doing pullups.
If you want for the regs on that conduit, look for conduit support spacings, looks like you have about 2 m run with no supports(no compliant), then white pvc is not good in sunlight(not sure about regs on this one), and then I see this conduit being a good support for some numpty doing pullups.
Not read entire thread,so sorry if this is a numpty question,but with bonding in mind.
A new 6.omm swa has been run with an additional seperate 10 mm earth cable for bonding ?
Why did you not just upsize the swa to 10mm ?
Have you checked to see if the frame needs bonding?
nothing to say that the 10mm bonding you have extended.....cant also be the PME that you export....in other words....just take the 10mm into the sub boards MET....then out to extranious....1 more question regarding this damn garage again!! Right carried out the swa/ducting plan. Obviously he'd already measured off the 10mm earth so I had just run it in with my swa, anyway the garage door has a steel frame down each side, bolted to the wall, sitting on very small wooden stilts then onto concrete, this is going to need bonded I assume but the 10mm earth only goes a far as the garage cu, is the bond to be continuous from the house or is from the garage cu to the steel adequate? Last question on this subject, I promise.lol.
Anything less than 22 k ohms needs bonding
????Cheers. So just pull the house fuse, do the IR then take it from there if it needs bonded or not...