K
Ken77
I'm an not that familiar with TNCS systems at all, as almost every system I work on is TNS. My question is this, is there a way to tell if a system is in fact a TNCS system. There is one I am currently working on which is labelled as PME, but rather that taking it as gospel that this means it is a TNCS are there any visual tell-tale signs, as I don't want to connect the earth to neutral if it is a TNS.
Thanks in advance.
Re: They say there are no stupid questions but I might be about to disprove that - PM
refer to earthing diagrams in on site guide or mant other electrical books
Why would you be connecting the earth to neutral anyway?
Reactions: 2 people
Thanks in advance.
with TN-C-S...both prospective short circuit current (PSCC)....and prospective earth fault current (PEFC) should be largely the same....
- - - Updated - - -
dont forget a TN-C-S uses the neutral as the earth path....
niceic snags and solutions earthing and bonding book all you need to no about earthing arrangements
If it's PME he would.
I always thought the neutral and earth should only be connected on the DNO side and only the DNO should be connecting them.
Reactions: 3 people
yes...otherwise you would have a TN-C system.....not allowed in the uk....
Glen to pick up on two points
Firstly PSC is 27a and PFC is 1483 a. Would this make you wary that PME label is incorrect?
Assuming it is a PME system (TNC-S) should I be getting the DNO to connect the earth.
glen to pick up on two points
firstly psc is 27a and pfc is 1483 a. Would this make you wary that pme label is incorrect?
Assuming it is a pme system (tnc-s) should i be getting the dno to connect the earth.
pscc=27a????
- - - Updated - - -
whats your Ze?
Yes, 27a as PSC and 1483 as PFC.
ZS - is 8.59 ohms. Which is high and a fail I know, under anything other than a TT, which it isn't. (Yet anyway). Currently arrangement is that what probably a PME system which has never had main earth connected to it, and instead is clamped to metal piping surrounding the incoming supply conductors.
I might redo PSC tomorrow to be sure.
With regards to above, would you believe the PME label? And if so, would you connect the earth or request DNO to do it?
first check your readings. then call DNO .
Reactions: 1 person
you cant make any assumptions on values like that Ken....as Tel here....
Last thing, and I really appreciated the advice - in any case is always the DNO responsibiliy to connect earth to PME system.
Thanks again.
Ken
whats this about connecting earthing up to DNO equipment Ken?.....
Thanks again.
Ken
yes it is...
Cheers, thanks alot.