Discuss Upgrading my garage supply. in the DIY Electrical Advice area at ElectriciansForums.net
See Appendix 15 BS7671 regarding Ring Final Circuits, with specific reference to SPURS
Had a read, I would argue that installing a small CU would be providing the same level of protection a fused spur would.
Just because it's not the norm, does not make it wrong or unsafe. All cables would be sufficiently protected.
Would I do it in my own house? No, I'd run a new supply from the CU.
Indeed, and using 2.5mm cable for them.
I said: "1.0mm is all that is required for lighting circuits." which he is also adding to.
If the circuit in the garage is protected by a 13A fused spur in the house then 1.5mm² cables will suffice for all. In fact, I would hazard a guess that you may find that 1.0mm² depending on the installation method may also do the job.
Reply to Upgrading my garage supply. in the DIY Electrical Advice area at ElectriciansForums.net
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Howdy, I'm looking for help with my plan to install an extra internal double socket and an external double waterproof socket to my garage. I...
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...