Just pointing out it’s in my opinion to test the circuits individually as the bigger the installation and circuit numbers then the lower the resistance in terms of going a global test
The whole point is that it's lower though. BS7671 requires the installation/distribution circuit with final circuits connected to exceed the minimum values rather than individual circuits. Strictly speaking the quoted values are for initial verification though. No particular value for periodic insulation testing is mentioned.
 
That problem won't disappear if you test them individually though as the requirement is for the insulation of the whole installation or DB to be above the values and not simply each circuit.
A quick way of doing IR testing on a 48 way 3 phase board?....Global test below 1Mohm, C2, installation fail.
May get pay for an extra day or two on remedial work...on top of the initial quote, I suppose.
No wonder I get undercut.....:rolleyes:
 
A quick way of doing IR testing on a 48 way 3 phase board?....Global test below 1Mohm, C2, installation fail.
May get pay for an extra day or two on remedial work...on top of the initial quote, I suppose.
No wonder I get undercut.....:rolleyes:
Exactly!
 
The whole point is that it's lower though. BS7671 requires the installation/distribution circuit with final circuits connected to exceed the minimum values rather than individual circuits. Strictly speaking the quoted values are for initial verification though. No particular value for periodic insulation testing is mentioned.
I stick with 1 Mohm personally.
If the overall value is lower than this then I code it
 
I agree, I wouldn't stop the inspection
I meant halting the inspection.
It is a legal requirement EAWR and H&S. That is to make safe where dangerous conditions are found, with the agreement of the person ordering the work. Common sense should tell anyone if you find a dangerous situation such as a possibility of electrocution due to touch voltage being present at a hazardous level you would (?) rectify it??? or not. I certainly would out of consideration of the safety of others, hang the legal implications it is just horse sense.
 
  • Like
Reactions: ruston
A quick way of doing IR testing on a 48 way 3 phase board?....Global test below 1Mohm, C2, installation fail.
May get pay for an extra day or two on remedial work...on top of the initial quote, I suppose.
No wonder I get undercut.....:rolleyes:
Lets say that you measure 20 circuits at 10 Megohms each. The fact is these resistances are in parallel so would you wrongly consider that to be OK in spite of the fact that the requirement in BS7671 is for an installation/distribution circuit with all final circuits connected and not for any one circuit?
 
Lets say that you measure 20 circuits at 10 Megohms each. The fact is these resistances are in parallel so would you wrongly consider that to be OK in spite of the fact that the requirement in BS7671 is for an installation/distribution circuit with all final circuits connected and not for any one circuit?
That’s why we are tought the 1/Rt method of calculating the total resistance in parallel.
Scientific calculator at the ready ;)
 
I am puzzled. 157v on braiding? Is that not a real and immediate risk of electric shock? If so would it not warrant a C1. In which case the person ordering the work should be informed in writing and the inspection halted until that situation has been dealt with???
Hopefully this will be an induced voltage (if braid left floating say). Perhaps the 2 pole voltage tester will be helpful?
 
  • Like
Reactions: DPG
BS7671 requires the installation/distribution circuit with final circuits connected to exceed the minimum values rather than individual circuits.

Then why do the model forms provide individual boxes to record IR for each circuit? If they had intended us to measure and record global tests then surely the model forms would reflect this?
 
  • Like
Reactions: Vortigern
Then why do the model forms provide individual boxes to record IR for each circuit? If they had intended us to measure and record global tests then surely the model forms would reflect this?
My understanding is that the boxes were intended to look nice. Hard to believe but apparently true. You could ask the same of the RCD test boxes. If the RCD is an RCCB it is likely to be protecting numerous circuits.
 
That’s why we are tought the 1/Rt method of calculating the total resistance in parallel.
Scientific calculator at the ready ;)
But that will give you an equally poor result than measuring the DB in parallel.
 
My understanding is that the boxes were intended to look nice. Hard to believe but apparently true. You could ask the same of the RCD test boxes. If the RCD is an RCCB it is likely to be protecting numerous circuits.

But for RCBOs it is necessary to have individual results, which covers the majority of installations outside of domestics.
Where does this understanding come from because it is quite hard to believe?
 
The insulation resistance of a conductor is inversely proportional to its length that is, its insulation resistance decreases as the conductor’s length increases and vice versa. It follows that the insulation resistance of a complete electrical installation, or a section of it, will be less than that of a single circuit of that installation.
Global testing a large installation will mostly give you relatively low IR readings.
There’s no format to insulation resistance testing other than the overall resistance of the db circuits and any distribution circuit applicable to said DB is 1M ohm or greater.
The method you test it is down to the individual.
 
The insulation resistance of a conductor is inversely proportional to its length that is, its insulation resistance decreases as the conductor’s length increases and vice versa. .

To a point. But in practice, any length of new cable will have an IR of pretty much infinity, at least as far as any normal test equipment goes.
 
To a point. But in practice, any length of new cable will have an IR of pretty much infinity, at least as far as any normal test equipment goes.
It was more to do with carrying the test out during a eicr on larger 3 phase DBs.
 
Lets say that you measure 20 circuits at 10 Megohms each. The fact is these resistances are in parallel so would you wrongly consider that to be OK in spite of the fact that the requirement in BS7671 is for an installation/distribution circuit with all final circuits connected and not for any one circuit?
That depends on how far you want, or need in some instances, to break things down. As the thread indicates, 'your opinion'. There's an argument to every opinion... we can all pick straws.
 
Where does this understanding come from because it is quite hard to believe?
From someone who was senior with the NICEIC at the time, as quoted on the IET forum on numerous occasions. (I don't know him personally.)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
Business Name
HomeCert Ltd

Thread Information

Title
Commercial EICR - Your opinion?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
HomeCert ltd,
Last reply from
Risteard,
Replies
37
Views
4,077

Advert