this has been bugging me for weeks..........
been using Fp200 for all socket / lighting circuits on current project , the usual 1.5/2.5 stuff
and im almost sure , but not 100% , that the tinned solid core cpc is the same size as the L / N ??
its certainly not a 1mm earth in the 1.5 cable......
had a quick nosey on a cable website but found nowt conclusive.
anyone else confirm or know different ?
 
perhaps because it isnt as good a conductor as copper they use the bigger csa size in order to keep earth loop impedance down ??? ( just a though)
 
  • Like
Reactions: 1 person
thanks ian but still doesnt mention cpc size like the other cable website i checked.

i can only deduce that the cpc is the same csa as line as a reduced size would need to be noted in the manuf. data.

something needs to be recorded on the cert for earth size so im going with my gut.
 
Can't you measure the diameter with a vernier and manually calc the CSA?

nope , got no verniers..........
but i could measure resistance on a spare piece - if E csa = L csa , then L-N & L-E should be the same on a continuity test :-)

i just thought someone may have come across the same issue previously , especially when the time comes to fill in cert and youre not on site lol.
 
i just thought someone may have come across the same issue previously , especially when the time comes to fill in cert and youre not on site lol.
I haven't seen a similar question so they've probably just made a wild guess :)

The resistance method would be pretty accurate especially if you have a longish piece of cable you could also size it using reference tables for copper wire resis/meter.
 
Check manufactures data / your cable supplier, it's no good just being "almost sure" now come on get a grip.
 
Fire Resistant
Red
100m
1.38mm (Strand)
100m
Three Cores of Plain Annealed Copper 1.5mm²
1.38mm (Strand)
12.1ohm/km@20C (Conductor)
300-500V

PS Tinned copper is better than plain
 
  • Like
Reactions: 2 people
Same size

i knew it ! lol , just thought i'd kill time with the ensuing debate. ;-)
marvo's right tho , never seen it mentioned in any other topic which is strange considering its wide range of applications / uses.
 
Is the earth core smaller when you use one of the cores in a SWA ? :innocent:
 
  • Like
Reactions: 2 people
perhaps because it isnt as good a conductor as copper they use the bigger csa size in order to keep earth loop impedance down ??? ( just a though)
no....do you not think the terminal screws wouldn`t get through the tinning?
 
A very good question I thought and to answer it the bare conductor is the same size as the sleaved pvc conductors Biff
 
  • Like
Reactions: 1 person
I've also come across this when doing a eicr, the lighting circuit in the cellar was in 1.5mm fp200 with a tinned copper 1.5mm cpc, the radial sockets however were fed with a 2.5mm fp200 cable with a 2.5mm stranded tinned copper cpc.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Need 2nd opinion on cable.......
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32

Advert

Thread statistics

Created
Guest55,
Last reply from
tidyboiler,
Replies
32
Views
5,736

Advert