D

DannyGouldson

I have a 10mm 4 core glanded into a length of conduit buried in the wall, around 2 metres in length, I tested continuity between all cores and galv conduit and it's perfectly clear, however when I tested IR it failed between 2 cores and conduit. Am I missing something here or does it simply need replacing? Cheers


---
I am here: http://maps.google.com/maps?ll=54.089885,-0.199081
I am not a number! I am a free man!
 
is either core earthed? are you getting a false reading from a neutral to earth due to parallel paths?
 
possibly not picking up fault on continuity due to low test voltage,if your doing IR test them you have 500 volts going through,try doing your continuity using the same setting as your IR test it,s suprising what doesn,t show on a continuity that an IR picks up.thats why we do IR test at twice the working voltage. hope this clears things up
 
Can I ask why you did a continuity check between cores and conduit in the first place, what was you hoping to achieve
 
I have a 10mm 4 core glanded into a length of conduit buried in the wall, around 2 metres in length, I tested continuity between all cores and galv conduit and it's perfectly clear, however when I tested IR it failed between 2 cores and conduit. Am I missing something here or does it simply need replacing? Cheers --- I am here: Google Maps I am not a number! I am a free man!
If the IR is low or you get a dead short, check if they haven't driven a nail through. ... or any bare leads touching the galvanised conduit.
 
Last edited:
Cheers guys the cable ain't terminated either side, I ran it in myself, I dont know what prompted me to test it in the first place but kinda glad I did, I guess I'm gonna have to replace it though since the insulation ain't upto scratch, just can't see why it would fail IR unless it's a manufacturing issue?


---
I am here: http://maps.google.com/maps?ll=54.089741,-0.199005
I am not a number! I am a free man!
 
just out of interest, what IR reading did you get?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
10mm armoured need replacing?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
DannyGouldson,
Last reply from
DannyGouldson,
Replies
7
Views
1,626

Advert