Hi All, some advice required please. I am in telecomms but need to have some wiring work done by a sub-con but want to check it's ok first.
I need to install 6 CB's but have no room in the MDB:
MDB = MCB63A with SPD, 2x16A, 2x6A (one of the 16A is spare)
Can I install an ACPDB next to the MDB to extend the CB's?
Plan is to install a 32A CB in the MDB in the existing 16A (swap 16A to 32A)
Wire the 32A CB in MDB to a main CB in the PDB of 32A and then have 6xCB in the PDB for equipment. (equipment is less than 4A each unit)
Wire the PE and N bars direct to between the MDB and PDB
Does that sound clear enough? and is it ok to do just like that or is a new mains in cable needed and a completely new MDB (expensive)
Thanks for anything in advance
S
I need to install 6 CB's but have no room in the MDB:
MDB = MCB63A with SPD, 2x16A, 2x6A (one of the 16A is spare)
Can I install an ACPDB next to the MDB to extend the CB's?
Plan is to install a 32A CB in the MDB in the existing 16A (swap 16A to 32A)
Wire the 32A CB in MDB to a main CB in the PDB of 32A and then have 6xCB in the PDB for equipment. (equipment is less than 4A each unit)
Wire the PE and N bars direct to between the MDB and PDB
Does that sound clear enough? and is it ok to do just like that or is a new mains in cable needed and a completely new MDB (expensive)
Thanks for anything in advance