Hi all,

Just lately I have seen this quite a few times: a 4 core SWA (cores brown, black, grey and blue) feeds a single phase distribution board. The spare grey conductor has been taped up with green/yellow
tape and used as an earth conductor. The steel armour has been bonded to the metal enclosure of the distribution board.

According to tha colour coding it is a fairly new installation and certainly not good practise.

I always thought you have to run a seperate (green/yellow) wire for earth if the SWA hasn't got one
and if one is needed at all and you are not allowed to use other than green/yellow cores as an earth.

I couldn't find it in the regs but somehow I seem to remember that you are not allowed to tape up
wires with green/yellow and use it as earth (although I might be wrong)

Can anyone help me with that? It looks like a bodge job to me.

Thanks guys.
 
You can use any colour you like provided they are suitably identified as to what purpose they serve.

Havent got my regs with me at the mo, but im sure someone will be able to give the number.

:)
 
To the best of my knowledge you can designate a conductor as a cpc (usually the grey) and all is well. You cannot however use a green/ yellow (or unsleved) as anything other than a cpc though since that is a specific designated use.

Also below a certian size the armout on a SWA can be used as the cpc so a 2 core would be fine.
 
I seem to recall somewhere that there is a standard for sleeving 3 phase SWA for single phase to avoid black being used as a neutral conductor:
Brown- left as it is
Black- sleeved Green/Yellow
Grey- Sleeved blue
May have even been the NICEIC but could be wrong.
 
Yes....there was a "de-neutralising the black" article in a connections newsletter when the colour changes first came in.
 
Dont forget for the swa to comply if used as earth as well there should be bonding link (fly lead) from the earth ring to the earth block and as for the cores been utilised as earth i agree with the above as long as its correctly marked along its full exposed length.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
any conductor as protective earth
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
stef,
Last reply from
Darkwood,
Replies
7
Views
1,951

Advert