Gossy

I have installed a new cooker supply to the new DB. The cable is a 10 mm T+E. It's on a 50 amp RCBO. (Big cooker!!) tested the cable and made put it in connector block and switched it on. I was getting 240v down live to earth which is correct but neutral to earth is was getting 40v. Then live to neutral I was getting 118V . I thought it was thought it was the RCBO but changed it three times and still read the same. When I connected it to cooker I get 240 v through neutral and earth as well as live and earth. What's going on???
 
think i'd be doing R1+Rn as well.
 
  • Like
Reactions: 3 people
I would carry out a R1+Rn test as well. Why did you change the rcbo 3 times?

EDIT: Tel beat me to it!
 
I'd be looking at the links in the terminal block in the cooker.
 
  • Like
Reactions: 3 people
i'd also query the use of 10mm cable and 50A MCB.
 
  • Like
Reactions: 2 people
there is something amiss with a neutral connection there some where like has been said r1 rn should be carried out
 
  • Like
Reactions: 1 person
More of a bizarre post than voltage readings
 
  • Like
Reactions: 1 person
Check the connection of the earth and neutral cables
 
  • Like
Reactions: 3 people
Hi Guys, between N+E the max voltage should be at max 2V, so this sounds very much like a broken neutral somewhere or a badly connected neutral at the CU. my first test would be to check this out. I have this as a common problem here in Africa, especially when we have to use auto transfer switches between the mains incomer and the standby generator and the contacts become pitted and carbonized. So turn off each circuit at the CU, then test for a V between N+E, if it has stabilized and you are getting the correct readings turn on each circuit one by one until you identify the circuit that is giving you the problem.
Hope this helps.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Bizarre voltage readings
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Gossy,
Last reply from
Biff61,
Replies
15
Views
2,271

Advert