Mark42
Patron
May 8, 2010
443
346
3,178,831
UK
Other
Good morning and a very happy lockdown to all :)
I'm using this tedious 'holiday' to fit a new suspended grid ceiling in my large open workshop.
Here's the provisional lighting plan, using drop-in 600 square LED panels from TLC. I have three existing circuits available (currently feeding 5 x 400W metal halides, which will be disconnected.)
Depending on the work in progress, I'd like a selection of lux levels, without the trouble and expense of using dimmable panels. So I'm fitting three separate circuits. Sketch and specs below.
Have I missed anything please? Has anyone done it like this before? (I'm new to LED panels).
Any comments/ideas before I build the thing?
Cheers, Mark
ps. (Of course the psychedelic colours are only to make the individual circuits easy to visualise. All panels are 5000K :cool: )
TL;DR
Best layout for multiple LED ceiling panel lighting circuits
That’s well thought out, and with that amount of lights, I wouldn’t go with dimming panels either.
Stick to the psychedelic colours though ?
Some led panels have 2 power inputs, allowing you to run the panel at half power
Just something to think about
In principle it looks and sounds fine. Depending on what work is being done in there. For instance if colour is important you might want to consider higher CRI factor. It sounds like you will be doing officey things in there? If so you need to get lights which have a UGR of 19. You need to know in advance the lumens deliver to desks, assuming there will be desks from your descriptions. The one big factor you need to work out is what is the inrush current. That amount of lights will struggle not to blow the MCB due to inrush. You might need to split them up circuit wise. You do not seem to mention emergency lighting or anti panic (required in a room that size. Just a few thought for starters. By the way I do a lot of commercial LED retro fit and upgrades. Oh and I don't personally like the asymetric nature of the layout.
Reactions: GBDamo
my thoughts are that that is a bit of overkill.
my design , numbering the rows 1-13, topto bottom:
stick with row 7 centre line; move row 5 to row 4 and row 9 to row 10; ditch row 3 and row 11:
9 less fittings.
3 circuits, 2 of 9 lights and 1 of 10.
and as vorty says, i'd line them up vertically.
Looking at it again I think you need to come away from the edges of the wall/ceiling. The angle of the spread of the light (120 degrees?) works better away from the wall in delivering lumens/light as it bounces off of the wall better when at least one tile away from the edge. The spacing is right in that there are three tiles apart longwise/widthwise. You might consider if there are any people who have eyesight problems as sometimes I have encountered reactions to lighting in the high K range.
all but one are 1 tile away from walls in his drawing.
True the tiles are one away, the red legend should move two away in line with the others. I don't know if I am reading it right but it looks as if the edge tiles are not full tiles, part tiles by the seeming look of it.
p.s. what height are the ceiling intended to be?
good point.
Reactions: GBDamo
Thanks for all the ideas. Quick lunchtime reply as I’m working on the building wall cladding today.
Finished ceiling height 3m exactly.
Perimeter tiles north and south are 500 deep, ie nearly full tiles.
Building use mainly mechanical engineering and maintenance by me, but is also rented for office/lab-type research work, with up to 20 people for a couple of weeks. Maybe I should consider warmer lighting?
But I have old eyes and always used intense MH lighting for very detailed work.
I wonder what a mix of warm and cold looks like? To offer a choice at up to about 300+ lm/m2. Naa, too complicated.
The great thing about these drop-in tiles is that I can experiment. But I’d rather do it only once!
I’ll follow the suggestions and draw up some other designs tonight and post. Thanks all for the brilliant help. I'm working alone and miss having second opinions available (even if only to ignore them.) ?
  • Funny
Reactions: telectrix
Acid house? How very 90’s ???
A quick question if I may.
If Lux falling on a target surface is a factor of source Lumen output, beam angle and distance from source, do you add together the Lux delivered from different sources where the beam patterns overlap?
My understanding is if a source of 5000 Lumens and a beam angle such that it liiuminates a target surface of 10m² would give a Lux level at target of 500 Lux.
If your lights were set in a pattern so that there was a perfect overlap, would the target Lux now be 1000?
Hi @GBDamo Two things, the required lux at the desk is something like 15 lux, second law of inverse squares applies. LED lumen output is prodigious and far exceeds (at 2.5-2.8m high) requirements for lighting in offices. Roughly speaking at 2m high the diameter of the spread of light is 2m. at a 90 degree cone of light. Therefore lights at three tiles apart gives approximately the right spread at say 2.5m without much overlap of significance. Inverse squares mean the amount of radiation received on a surface is inversely proportional to the sq of the distance away. So light drops of quite steeply at greater heights.
Thought an office was 450 Lux?
Anyhow, I don't think its too complicated when thought through logically.
The OP has 29 panels at 0.6m² each at 4000 Lumens, total 17.4m²
The workshop is approx 140m².
So (4000 x 17.4) /140 =497 and bits..
This should give in the ball park of 500Lux.
Be interested to see how far off my smoke packet maths is ?
The perception of colour is unimportant.
Most of the work which matters will be scientific research type stuff, with people and machines. A desk or two for recording research results, but mainly people milling about.
Good point about inrush. These fittings from TLC are soft start so I'm guessing a 3P B6 MCB will be fine. Each of the three circuits would be on a separate phase anyway.
A few fittings will have emergency back up batteries. I didn't mention that for clarity.
I've never heard of 'anti-panic' ... My industry mitigates that risk not by engineering contols, but by excluding the kind of people prone to panic :)
Good points about glare. I have bought one 5000K panel, and it looks OK - very evenly lit - unlike the point-source retina-busting nature of many LED fittings. Despite that I've now changed to spec to 4000K panels.
One guy did complain last week in another workshop about the unnatural quality of the light from my metal halides. But he was a techie physicist dude much given to speculation on the psychological effect of discontinuous spectra, so I ignored him. ?
You and Telectrix have caused me to have a rethink. Thanks! Here's a new plan:
I'm slightly concerned that this might not be bright enough. It's theoretically 610 lux with all on, but it is a high ceiling at 3m: the inverse square law is a bugger.
This new design allows for the easy addition of another 13 panels on the red circuit at the red X positions if needed.
I'd originally used so many fittings, together with the weird asymmetric arrangement, so that any one circuit on alone would not be too patchy.
Cheers, Mark.
Are you sure about the lumen output on Yel and Blue? Anti panic is a description of the function of the emergency lights. i.e. there will be some light when all the lights go out instead of darkness. UGR must be specifically specified when purchasing the lights. They are a specific class of lights. You can ask the manufacturer if the lumen/Lx delivery will meet requirements in the environment you propose to provide lighting for. You can also ask them the inrush current characteristics of their lights. At the same time you can obtain the photometric date for the lights as well as for the emergency light fittings. In getting the photometric data you can prove, in the absence of a luxmeter, that the emergency/anti panic deliver the required lumens as specified by BS standards (5266). As well it is usual to supply circuits in 10a for commercial. Not entirely sure why that is, but of course not compulsory. Are you planning to use white 20mm conduit and Klix fittings for the install? And the new design looks a lot better by the way. What are the red crosses?
Are you (OP) trying to raise the lighting level for the whole area for detailed/inspection work or just specific areas?
We did a similar job couple years back where the overall/general level of lighting was high (>500lm) and just specific areas (Panels side by side) to raise level (>800lm) where detailed work was required.
Arrangement looks odd on paper but worked in practice - It was a small photographic/print works FYI.
Cheers, Mark.
that looks better to me, but should be more on red circuit, less on yellow and blue. and i would opt for 10A C curve MCBs on all 3.
Because no two jobs/rentals are the same I don't have the luxury of being able to install overall/task/accent lighting in fixed places. So I'm trying to go for two fixed levels (say 'normal' and 'bright') for the whole area.
As there are now so few fittings compared to my first proposal, I downgraded the third smaller circuit, which was only ever for dim overall lighting when popping in to get something. But I'll do as you suggest and change a few. See below ...
If I reduce the number of either 'yellow' or 'blue' panels in the new reduced design too much, there won't be enough left to be used alone to light the whole room, when high intensity task lighting is not needed. Hence the odd unbalanced design.
There's a further complexity which I didn't mention: the L2 circuit has a 'security lighting' relay across the switch. This is standard throughout all the buildings, all of which are interconnected with a 25-pr data cable, one pair of which carries +24Vdc from the alarm panel in case of an alarm activation. (Via a Texecom relay output). The effect is to blast every building, and a lot of the grounds, in light in case of an alarm, or if any panic button is pressed. So I need to be sure the L2 circuit has enough lights to frighten off, and to get a clear CCTv picture of any low life who breaks in thinking he'll find a quad bike to nick.
There's also the consideration that, for historic reasons, L1 and L2 have a solar supply, but L3 is paid-for only! This was all too much detail for my original questions.
And there's a technical reason why I want to at least try a 6A B-curve MCB first: I have a spare one in my box! ? If it trips, I'll do as you suggest and buy a new 10A.
Thanks. I already got the photometric data from the TLC site, everything else I'll decide by trial-and-error! These appear to be very evenly-lit panels, glare-free, with a 120 degree output angle.
No conduit, no. These are inset panels designed for a drop grid ceiling so all wiring goes in the void. I was intending to use T&E between Wago boxes. The panels come with drivers with short pre-wired tails, so that struck me as the easiest way. A single and earth provides the power failure signal for the emergency units. All wiring cable-tied along the grid. Is there a better, perhaps more modern way? The roof above is sprayed with horrible foam, so I can't get any neat conduit up there.
The red crosses are potential points to augment with more panels if the room's not bright enough!
ow are youplanning on supporting the T/E? hope you're not intending to just lay it on the false ceiling.
Maybe 'lighting distribution boxes' but if 'short' flex's from panel drivers do not reach then could become a more costly install.
Still need a supply to each box and I guess you are implying cable tying to the straining wires??
Not only modern but time honoured quality installation, conduit 25mm and Klix connections every time for me. None of that cables on the tiles/in the void very poor technique in my opinion. Besides if you plan the Klix points properly you can move and add lights with ease. With the void wiring when you want to rejig things you start ending up looking like spaghetti junction up there and it is confusing when you want to change lighting/switching, don't do it!
I don’t disagree. But to what do you fix all that beautiful neat conduit? (Assuming you do of course mean rigid PVC)
The internal roof structure is covered in 200mm of messy foam.
The drop ceiling meets the walls at the eaves, so there’s no room there either.
You fix them to the same thing you are going to fix the suspended ceiling to, non? At least you could use marshalling boxes?
Here are some pictures of today's work-in-progress.
Note the horrible foam insulation. I'm fixing the ceiling grid wires by making small holes in the foam, finding the metal purlins, fixing brackets with Tekscrews, then filling the hole with a foam gun. Only the small office is done so far. There are a couple of trial LED panels in there: one 30W the other 40W.
There's no way I can think of to get neat conduit up in that roof. Hence my proposed bodgers' delight method of running cables along the grid. I may use Flexishield, or run T&E in flexible 20mm (TLC have good deals on 20mm flexi, I use it a lot.)
What would others do, given the job of wiring a shed-load of light panels in this suspended ceiling?
Tray hung on threaded rod from the purlins right down the centre.
Cables on the tray, marshaling boxes fixed to the underside.
The flange on the purlins is very flimsy, and not horizontal, but it could be done, so long as any lock nuts are not fully tightened, to allow the studding to hang vertically.
BUT ... How would I then get individual cables from the minimum 23 panels to the marshalling boxes? Might that not be more of a rat's nest that runnning the three supply cables directly as single radials looped to each fitting at ceiling level?
Girder clips on the girders for conduit at each girder with a marshalling box on each girder. No it wont be a rats nest. And as stated earlier if you don't like the final outcome it is easy to change.The point being that change is possible with marshalling boxes. It wont be anywhere near as bad as cables where it is a right kerfuffle sorting out what cable is what when they are bound together. I've seen it and had to struggle with it, it is a nightmare. Later on in the life of the installation it will change. You will thank us you did it right when you have to change out the panels (which you will) with a five year life. No doubt you will have comms cables up there as well? So I would put enough Klix fittings to allow for extra panels and ultimate flexibility.
p.s. dont glue the conduit together.
Crikey did that really take me three months to get around to finishing this? ?
For those who like to see the finished job, here's my workshop ceiling. Pretty standard stuff I guess, but a massive improvement on the tatty uninsulated space it was before.
The proposed LED panel lighting layout (across three circuits) works absolutely fine. I'm convinced by these panels and will never use fluorescents or LED striplights again.
BTW, repeatedly slamming all three switches on together does not trip the 6A(B) breaker. There are no inrush issues.
Thanks again to those who took the trouble to offer advice.
View attachment 84007View attachment 84008
that's exactly how i would have done it as regards positioning. 3 tiles between rows and 3 tiles between fittings (unless there is a need for higher levels of lux). I done 3 Spar shops on this basis and light levels were better than the 1200 x 600 florrys that they replaced. now show us a photo of what's above that suspended ceiling. ??
Nice job, my only small critique which others may or may not agree with is that light by the door, it would imho be better without as the fitting close by ( not lit for some reason ) would have provided plenty of light to cover that spot.. it just makes the nicely arranged layout look a bit off in that corner especially been against the wall itself.
Like above, I do a similar layout, either 3 by 4 tile or 3 by 3 tile plan depending on light level needed and ceiling height, given the number of outlets on the wall I expect this to be a work area and totally agree on the 3/3 tile arrangement.
Mark42
Patron
UK
Other
Ceiling design for 600x600mm LED drop-in panels please.
Lighting Forum
Mark42,
Darkwood,