BecciG1978

I’m hoping someone can help. We recently had an extension built to house a working kitchen for my new business. The original sparky wasn’t available to fit the oven when we arrived, so we hired another, who said he couldn’t install it as the wrong wire and fuse were fitted.
When the wiring & fuse was installed, I’d planned to use a 4.2kw double built in oven, but as it was not available, ordered a different one of 4.7kw.
Original sparky installed a 2.5 cable with a 40 breaker, the second sparky says we need a 6ml cable with a 32 breaker, and the manufacturer says it needs a 20 breaker. Which one is it?!!! Original sparky’s arguing with our builder saying what he installed is fine, second sparky says it’d be dangerous, could melt, and catch the house alight, which is obviously the last thing we want, especially with two young kids in the house. Help!!!!!
 
You cannot put 2.5mm2 cable on a 40A circuit breaker. The breaker is there to protect the cable, and the cable could melt before the breaker tripped.

However, the oven only takes approx. 20A. So you could have the circuit changed to a 20A circuit breaker, and it should be fine, depending on how the 2.5mm2 cable has been installed (how much insulation etc). The second sparky should be able to confirm if this is OK.

Is assuming with this that there is nothing else connected to this circuit (e.g. a hob) since you didn't mention anything else!
 
You cannot put 2.5mm2 cable on a 40A circuit breaker. The breaker is there to protect the cable, and the cable could melt before the breaker tripped.

However, the oven only takes approx. 20A. So you could have the circuit changed to a 20A circuit breaker, and it should be fine, depending on how the 2.5mm2 cable has been installed (how much insulation etc). The second sparky should be able to confirm if this is OK.

Is assuming with this that there is nothing else connected to this circuit (e.g. a hob) since you didn't mention anything else!


No, no hob, just the oven. The cable runs in a cavity between either cinder block or brick (depending on the wall), and the plasterboard, and the cavity between the ceiling plasterboard and the flat roof. No insulation in that cavity.
So as long as we replace the fuse with an appropriate one, it’ll be safe?
 
  • Like
Reactions: DPG
Thanks - having a quick read of the installation manual it does say-

5.1kW
20A
4mm cable

My guess is the manufacturer recommends a 4mm cable to err on the side of safety as the maximum current is likely 22A or less and 4mm will carry that in even the most adverse installations.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Clarity on wires and fuses for ovens
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
BecciG1978,
Last reply from
Wilko,
Replies
7
Views
1,956

Advert