Mr Mark Sparks

pir every 3 months on site supplys and cabin feeds not cabin internal circuits

thats what i thought

ive seen a saftey policy today that says if cabin sub mains come off a cabin internal cu they are exempt

thoughts please where are the recomended testing intervals
 
Section 704 of the red book says that the if the cabins are administrative locations (704.1.1.vi) eg offices canteens etc then they are not covered by the scope therefore my reading says that 3 monthly test not required. Check P181 of your book for more info.
 