Most terminals have a min-max range of what they are designed to reliably clamp. If your cable is below the minimum value you would have to double over or use a crimp pin, etc, to meet the manufacturer's specification.
But for most domestic CU devices I expect they are rated to clamp as low as 1mm for lights, etc.
Makes senseMost terminals have a min-max range of what they are designed to reliably clamp. If your cable is below the minimum value you would have to double over or use a crimp pin, etc, to meet the manufacturer's specification.
But for most domestic CU devices I expect they are rated to clamp as low as 1mm for lights, etc.
Thankfully no, other than the general requirement for good workmanship to be used. The regs are not there to teach the technique of being an electrician, that is down to the individual. Look at the terminal design and size, look at the number, size and type of conductors to be terminated, possibly even look at the manufacturers specifications. The using your professional skill and experience, choose the best method to make a mechanically secure, resilient, low-resistance termination in that specific scenario.Is there a regulation on this?