Hi all,

I'm not sure about this, but there is PVC conduit installed one side of a masonry wall and the KO boxes are on the other side of this wall, with the aim of the cables entering into these KO boxes from the back.

Now in my mind, conduit has singles in, not Twin + CPC, but I'm concerned about there being a bunch of singles going through the wall to the other side and there not being a sheathing to protect the individual cores.

Please could someone point me toward either the correct regulation or put it in simple terms what I can and cannot do.

This is not a question about safe zones (before anyone mentions them).

Thanks all,

Si
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

I hate singles ! 26 rewires in them grrrrrrrrrrrrrrrrrr have to admit i always slung some con through the wall !
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

I reckon our troll is back AKA the knob who was wondering why his elecs were tripping when he changed a double socket and linked everything out

IIRC it was deleted by mods, this will be soon id of thought (sorry this post was aimed at user " Faithmaster "

I'm sorry you feel this way, obviously I was only joking but I am neither a troll or a knob.
This seemed like an interesting forum to exchange a few ideas but hey ho...
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Anyway for what its worth of course you would need to put a sleeve through the wall, it is just good practice.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

If you could get away with just slinging singles through walls then all my efforts of threading 4" pieces of conduit have been wasted! Arghh!!!
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

If you could get away with just slinging singles through walls then all my efforts of threading 4" pieces of conduit have been wasted! Arghh!!!
Not really, you'd want metal conduit, to be continuous in most cases, as it's often a conductive-part.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Yeah I knows, only joking, I would never intstall singles just through a wall, conduit has to be a complete system.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Not quite sure of this one... Conduit installed, but can singles go through masonry
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
Mr.Si,
Last reply from
GLENNSPARK,
Replies
26
Views
3,400

Advert