I'm not sure about this, but there is PVC conduit installed one side of a masonry wall and the KO boxes are on the other side of this wall, with the aim of the cables entering into these KO boxes from the back.

Now in my mind, conduit has singles in, not Twin + CPC, but I'm concerned about there being a bunch of singles going through the wall to the other side and there not being a sheathing to protect the individual cores.

Please could someone point me toward either the correct regulation or put it in simple terms what I can and cannot do.

This is not a question about safe zones (before anyone mentions them).

Thanks all,

Si
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

The conduit must be continuous, so fit a piece of conduit through the wall linking 2 back to back boxes.

Or you could do a loop in system into loop in boxes.
 
Last edited by a moderator:
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Nothing stopping you from passing singles through a wall, as the wall will provide mechanical protection.
 
  • Like
Reactions: 3 people
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Nothing stopping you from passing singles through a wall, as the wall will provide mechanical protection.

Even if the masonry could hurt the singles when passing through? I suppose it just needs a bit of care and then the cables will forevermore be static.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

If you look at regulations 521 then you will see that they refer you to appendix 4 and table 4A1. Where non sheathed cables can only be installed within a containment system or onto insulators, so though it does not mention through walls directly I would interpret that you can not install singles cables unless they are enclosed in conduit, trunking or ducting.

Of course Bonding and main earth conductors can be.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Nothing stopping you from passing singles through a wall, as the wall will provide mechanical protection.

Try getting the cable manufacturer to agree to and guarantee that installation method.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Thanks gents.

I will have to work out how to get a bigger hole through the wall with the drill bits I have and send a bit of conduit through.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

If the conduit is 20mm then a normal 20mm hole will do nicely, unfortunately 25mm conduit requires about a 26mm hole as it is a bit snug.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

or a hammer
 
  • Like
Reactions: 2 people
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Maybe a bit of flexible conduit from the back of the through box to the knockout box would be a little easier.
 
  • Like
Reactions: 1 person
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Now there's a plan!

However, I was just thinking of running Twin & CPC through the conduit (there's only one length, as it's just 2 single gang sockets on a radial) and then put the inspection box over the hole and pass the twin&cpc through, which will be fine.

Many options!
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

i'd stiil shove a bit of tube through the wall. what if the brickworms start eating the cable ( if you take this seriously, you should be on the screwfux forum.LOL.)
 
  • Like
Reactions: 2 people
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

I would always insist that any cable system passing through any type of wall or structure, should be done so by means of propriety electrical enclosure system such as conduit etc, or in the case of multi cored cables etc, by means of a sleeve... In the case of fire walls and slabs in commercial/industrial installations, any form of electrical wiring containment or cable sleeves, will need fire rated sealing/barrier each side of the fire wall....
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Or through crimp the singles to some flex and push that through the wall.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Thanks gents.

I will have to work out how to get a bigger hole through the wall with the drill bits I have and send a bit of conduit through.
Right ...in my eyes a solid wall would constitute "mechanical protection" .....so why not just tape em up as they go through the wall (if you think they might be damaged pulling them through........or buy some bigger drillbits/steels....!..lol..:44:
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

I reckon our troll is back AKA the knob who was wondering why his elecs were tripping when he changed a double socket and linked everything out

IIRC it was deleted by mods, this will be soon id of thought (sorry this post was aimed at user " Faithmaster "
 
Last edited by a moderator:
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

i'd stiil shove a bit of tube through the wall. what if the brickworms start eating the cable ( if you take this seriously, you should be on the screwfux forum.LOL.)
But I am.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Right ...in my eyes a solid wall would constitute "mechanical protection" .....so why not just tape em up as they go through the wall (if you think they might be damaged pulling them through........or buy some bigger drillbits/steels....!..lol..:44:

Reg 521.10.1
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

I hate singles ! 26 rewires in them grrrrrrrrrrrrrrrrrr have to admit i always slung some con through the wall !
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

I reckon our troll is back AKA the knob who was wondering why his elecs were tripping when he changed a double socket and linked everything out

IIRC it was deleted by mods, this will be soon id of thought (sorry this post was aimed at user " Faithmaster "

I'm sorry you feel this way, obviously I was only joking but I am neither a troll or a knob.
This seemed like an interesting forum to exchange a few ideas but hey ho...
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Anyway for what its worth of course you would need to put a sleeve through the wall, it is just good practice.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

If you could get away with just slinging singles through walls then all my efforts of threading 4" pieces of conduit have been wasted! Arghh!!!
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

If you could get away with just slinging singles through walls then all my efforts of threading 4" pieces of conduit have been wasted! Arghh!!!
Not really, you'd want metal conduit, to be continuous in most cases, as it's often a conductive-part.
 
Re: Not quite sure of this one... Conduit installed, but can singles go through mason

Yeah I knows, only joking, I would never intstall singles just through a wall, conduit has to be a complete system.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Not quite sure of this one... Conduit installed, but can singles go through masonry
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
Mr.Si,
Last reply from
GLENNSPARK,
Replies
26
Views
3,367

Advert