Discuss Recommend where to buy a G59 Relay in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
F
FIT-PV
I have a 100KW installation coming up next month. The DNO require an additional G59 relay to be installed, although the inverters are G59 already. I was just wondering if anyone recommends a good place to buy one.
I have 5 Mastervolt CS20TL inverters that will be installed. Is it just the one relay that will be required?
As they all say above Andy's your best man!
Yes Just one 'relay' is what is required, it disconnects the grid when the grid parameters are out of the G59 spec.
In this instance you will also almost certainly need professional commissioning as I don't believe they are 'type approved', as such you may also need witness testing - Andy can sort all that for you.
Give DEIF a try - they are manufacturers of the relays so know them better than anybody - they also do professional commissioning at good rates - delivery is quick and they are usually flexible for dates of commissioning - 0161 429 4940 - based in Manchester.
Reply to Recommend where to buy a G59 Relay in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
14K
Greetings, I have a solar 5kw system installed with a hybrid inverter (no batteries yet). My electrician decided to add an extension board for the...
5K
Hi, sorry if this has already been discussed or is in the wrong place. Im wondering if anyone has come across a domestic EV charger where the ct...