Hi all, been rewireing lighting in house and fitted new CU but whilst there found the cooker switch and socket are too close to cooker ie level with edge of it.
What I want to know is as the client don't want to move it what do I put on installation cert as it is a non compliance? thanks in advance
Paul
 
Hi Solo,
Your EIC will only cover the lighting circuit and new CU.
Even though you are testing all the installation, as you have put in a new CU, you are not doing a periodic and so the socket is not part of it.
You can advise the customer, but you cant fail it (code1 or 2), as that was probably put there for years before the current regs.
Hope this helps,
Sav
 
On the EIC, you have a box labelled 'extent of the installation covered by this certificate' in that box, you write 'consumer unit replacement only'.

This then limits your responsibility to exactly that and as Sav said, the offending item has probably been there for years without ill effect so even on a periodic, it would only attract a code 4.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
socket over cooker
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
solo2771,
Last reply from
IQ Electrical,
Replies
2
Views
2,070

Advert