recently changed an old fuseboard to a new MK consumer unit with 2rcbo's and then RCD with 5 mcb's on it, now i IR all the circuits and all came out at <299Mohm but since day 1 the rcd has tripped whenever a high load is switched on? i tried the up and down ring and the fridge radial on 1 of the rcbo's (40A) and they worked fine but if i put them back on the rcd side they trip. anybody got any ideas? also the test button on the rcd isnt working, now this is the 2nd rcd ive tried as i changed the 1st 1 just incase that was faulty.
 
Did you test for an earth?

seems like a odd one, one of them " have to be there ones " haha

Good luck, try the above suggestion though
 
seen something similar once before, could be reverse polarity somewhere.

everytime customer used hoover rcd would trip. located mixed connections in thermostat which plumber had connected
 
have several times found where customer has replaced a socket face and has reversed N/E. as soon as a load is applied, the RCD will trip.
 
easier way would be to interconnect live and earth and do r1 + r2 test at board and locate fault like that. you'll soon find where its been connected wrong
 
it may sound obvious but make sure the neutrals for the circuits connected to the RCD are indeed connected to the RCD it sounds as if a neutral is in the wrong place in the CU.
Test button should work if L and N are connected correctly check polarity at the incoming main switch on the CU. If LN ok and test button not working take it back and exchange RCD as faulty.
What type of earthing system is it?
What was the Ze ?
Did you carry out a full PIR and schedule of tests before changing the CU?
 
Did you notice anything strange about those boards?

Like the main switch has to be levered into the off position but flicks on!!

I had a similar problem last night, it was the fish pond pump.
 
no rcd before hand jus old wylex fuse board, got a borrowed neutral but sorted that at the moment by putting them in same rcbo till i can run a new cable. i tried numerous high loads such as tv, fridge, 3kw heater even me sds drill but all tripped it. i got a low ze cant remember reading i wrote it down and its with all me gear on a job, its just thrown me as this is the second rcd ive tried which makes me think its something on the installation.
 
When you carried out IR test I assume all loads were disconnected. It seems that there may be a leakage problems on the loads rather than fixed wiring, the old CU would not detect earth leakage on loads. PAT testing of the appliances that trip the RCD might help. If you cannot isolate one load as the cause it may be a cumulative effect IE 15mA leakage on more than one load.
 
Assuming that the RCD is OK, there's something wrong with the way the CU is wired if the test button isn't working (pressing it introduces a neutral -> earth fault at the RCD). That's what I'd be fixing before looking elsewhere. Check through all of the CU cabling connections (particularly the neutral and earth).

I assume that the IR readings where >299M Ohms ;)
 
"the test button isn't working (pressing it introduces a neutral -> earth fault at the RCD)."

Are you sure about that?
I always thought it was a purely mechanical test.
Alan.
 
"the test button isn't working (pressing it introduces a neutral -> earth fault at the RCD)."

Are you sure about that?
I always thought it was a purely mechanical test.
Alan.
Positive, thanks. What would be the point in testing quarterly an electronic device via mechanical means ?
 
Here's a little quote from the MK datasheet:

Where connection of a neutral supply is not
possible, then an alternative method of
ensuring that the test button is operational is
to fit a suitable power resistor (rating 4W)
between the load side neutral pole and a
phase pole not associated with the normal
test button operation
 
you could have a fault in a socket or an intermitant N to E fault it could be on any circuit not just the heavy load circuit as all the N's and E's are joined together on there bus bars they are common so although on low loads it doesnt trip on the higher it could increase the loading around the fault although just a tad but enough causing the RCD to trip ,oh and watch the main switches they have a habit of flipping on
 
i suspect a n-e fault somewhere, had one recently where rcd wouldnt trip and zs testing on ring failed with a trp message, found a low n-e fault to an outside light.
 
The test button does NOT introduce a L - E fault on an RCD
The test button is connected to the Line conductor on the load side of the RCD this is connected via an internal resistor to the feed neutral. Pressing the test button allows current to pass through the RCD in the line conductor through the test resistor and back to neutral on the feed side so the RCD sees a difference in line and neutral current inside the RCD and trips out. If the test button is not working check supply polarity is correct L-N if yes Take the RCD out and change it again ?
 
Last edited by a moderator:
Good drawing Tony
Bottom line There are 2 faults

1) The RCD wont' trip on test button operation - check supply to RCD - Test RCD on a known good installation (own house) If RCD wired correctly it should trip SEE Tony's post
If not tripping change it again

2) The RCD trips when loads are switched on
but not when no loads connected - appliance/load problems

PS long distance fault finding is proving quite difficult
 
Last edited by a moderator:
I agree with Tony and others... if the test button is not tripping the RCD, that needs sorting before any other fault finding, and the test button not working would be caused either by a faulty RCD unit, or incorrect wiring configuration within the CU (but I can't think what!).
 
I’ve just re-read this thread.

I’m sorry but for professional electricians some of you should sign yourselves as “Hop-a-long Cassidy”. You condemn cowboys, but then give advice that is so off target it’s a wonder you’ve got two feet left!

A RCCD is a simple thing to figure out, if what’s going in doesn’t equal what’s going out then you’ve got a down stream fault and it trips. If it doesn’t trip on the test button then the RCCD is faulty (unless you’ve used a 4 pole 440V unit).

Sort your testing in to logical order, it’s the only way to fault find.

Sorry but people rely on you to get things right, I wouldn’t be impressed with someone constantly on their I-Pad asking advice.

Don’t get me wrong, I’ll help anyone, but you have to have the basics. Not just being able to quote regulations ad nauseum.
 
I quite agree with Tony and patty1005. I've had similar problems in the past. The RCD detects an imbalance between the line and neutral on the load side and pressing the test button simulated this imbalance to cause RCD to trip. I guess a few guys were right too, in carrying certain test and in particular trying the RCD in a complete different CCU to check its functionality.
 
Where the hell do outside lights come in to it!

For gods sake it’s not difficult if the RCD fails to trip on test, the faults in the RCD.

View attachment 7289


Sorry Tony , but i have come across this before RCD trips on high loads brand new install ,the fault was caused by an incorrectly fitted lid on an outside light ,the light was half full of water ,replaced the fitting fault gone , this was the reason i mentioned outside lights
 
im sorry also Tony,

had a rcd that wouldnt trip, swapped for another exactly the same, swapped for the rcd in other bank which worked on one side but not the other.
removed all neutrals and it tested fine, replaced one at time until it stopped working when an old heating supply that had been fused down to supply an outside light caused the rcd not to trip and zs tests to fail, repaired the cable and then all tests came back fine.

But obviously I AM WRONG and as you say it was the rcd, next time ill leave it and tell customer the cu will only accept one rcd as all the rest in the world are broken................

and as a wise man once said and im inclined to agree with

I’m sorry but for professional electricians some of you should sign yourselves as “Hop-a-long Cassidy”. You condemn cowboys, but then give advice that is so off target it’s a wonder you’ve got two feet left!
 
Last edited by a moderator:
im sorry also Tony,

had a rcd that wouldnt trip, swapped for another exactly the same, swapped for the rcd in other bank which worked on one side but not the other.
removed all neutrals and it tested fine, replaced one at time until it stopped working when an old heating supply that had been fused down to supply an outside light caused the rcd not to trip and zs tests to fail, repaired the cable and then all tests came back fine.

But obviously I AM WRONG and as you say it was the rcd, next time ill leave it and tell customer the cu will only accept one rcd as all the rest in the world are broken................

and as a wise man once said and im inclined to agree with

Ok try that and if that don't work I'd go with the wiring beforehand haha

Maybe try the rcd connected with none of the mcb's connected? ( can't remember if this has been tried and am not re-reading all the posts again )

And as for the above..... Looks like a lot of us has learned something today :)

When removing all neutrals I'm guessing you mean with mcb's switched to off with the main breaker on?? Otherwise the neutrals would become live.
(just an apprentice and I like to be sure of these things!) hahaha 
 
RCBO's - They are the future!!! I got so fed up with RCD's and shoddy quality I only fit new boards decked out with RCBO's now, cost has come down so much its not all that much extra IMHO.
 
Please supply a better drawing.

William Heath Robinson was a fantasic guy, using his methods I’ve got umpteen industrial plants going. What’s wrong with a brush stale holding a circuit breaker closed?
 
Last edited by a moderator:
Just to make i clear Tony when i replied i was in no way having a go . it was just a scinario that i have come across , and the reason i mentioned the outside lights , electricity can do wird things and with the addition of RCD make the whole job more intresting
 
RCBO's - They are the future!!! I got so fed up with RCD's and shoddy quality I only fit new boards decked out with RCBO's now, cost has come down so much its not all that much extra IMHO.

But don't you need an RCBO for each circuit, as opposed to having a single RCD that covered a few? Or can you get RCBOs that can cover more than one circuit?

Cheers
 
Just to make i clear Tony when i replied i was in no way having a go . it was just a scinario that i have come across , and the reason i mentioned the outside lights , electricity can do wird things and with the addition of RCD make the whole job more intresting
cant see why not

this is one of the worst statements ive ever read lol
For gods sake it’s not difficult if the RCD fails to trip on test, the faults in the RCD.

 
But don't you need an RCBO for each circuit, as opposed to having a single RCD that covered a few? Or can you get RCBOs that can cover more than one circuit?

Cheers
You can, as with MCBs, put more than one circuit into an RCBO but it's not good practice. There's nothing wrong with mixing RCBO's, MCB's and an RCD(s) in a consumer unit if you want to achieve that (and have the necessary module space).
 
i know the wirings messy inside, but ive got no slack on any cables to try neaten it up so its the best i can get it. still havent got job sorted only just got access to property again



12082011964.jpg
 

Reply to trouble with newly installed MK c/u in the Australia area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
778
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Hi guys I have this problem that I've been trying to figure out all week. On friday I had a 5 tail economy 7 smart meter installed and every...
Replies
30
Views
7K
Hi Don’t often post on here but I’ve dreamt about this issue last night. Need advice please Yesterday I attended a property to complete an EICR...
Replies
9
Views
1K
Toneyz
T
Hi all, Any help would by greatly appreciated as i have tried everything i possibly can. Heres some info on the situation, installed some spike...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock