Noah Katz

DIY
Reaction score
3
I'm updating my kitchen wiring and I believe the in-ceiling ventilation fan needs to be AFCI-protected.

To accomplish this electrically all I need to do is pigtail into the hot wire of one of outlets on the load side of the AFCI outlet.

Can I just clip off the unused neutral and ground wires at both ends where the sheath ends, or do I need to wire them in normally (they would be redundant)?

Doing the latter would bring the allowable conductor volume just up to the limit and make stuffing all of the wires into the box even more of a struggle.
 
Last edited:
I'm updating my kitchen wiring and I believe the in-ceiling ventilation fan needs to be AFCI-protected.

To accomplish this electrically all I need to do is pigtail into the hot wire of one of outlets on the load side of the AFCI outlet.

Can I just clip off the unused neutral and ground wires at both ends where the sheath ends, or do I need to wire them in normally (they would be redundant)?

Doing the latter would bring the allowable conductor volume just up to the limit and make stuffing all of the wires into the box even more of a struggle.
Noah kitchens need to be GFCI Protected, all other rooms need AFCI Protection with the exception of the laundry room which needs to be GFCI Protected
[automerge]1590362297[/automerge]
Noah kitchens need to be GFCI Protected, all other rooms need AFCI Protection with the exception of the laundry room which needs to be GFCI Protected

If all you need is 1 conductor I suppose you could use one wire out of the NM just make sure the white wire is taped and it’s never a bad idea to go ahead and hook up the ground wire
[automerge]1590362315[/automerge]
Noah kitchens need to be GFCI Protected, all other rooms need AFCI Protection with the exception of the laundry room which needs to be GFCI Protected

If all you need is 1 conductor I suppose you could use one wire out of the NM just make sure the white wire is taped and it’s never a bad idea to go ahead and hook up the ground wire
 
@Megawatt

Noah kitchens need to be GFCI Protected, all other rooms need AFCI Protection with the exception of the laundry room which needs to be GFCI Protected

Yes, actually I'm using AFCI/GFCI outlets.


If all you need is 1 conductor I suppose you could use one wire out of the NM just make sure the white wire is taped

That occurred to me but I figured that removing the protective sheathing would violate code.
 
To accomplish this electrically all I need to do is pigtail into the hot wire of one of outlets on the load side of the AFCI outlet.

Can I just clip off the unused neutral and ground wires at both ends where the sheath ends, or do I need to wire them in normally (they would be redundant)?

How does the extractor get it ground and neutral? The neutral must come from the same circuit as the hot.
I can't speak for the rules in the USA but common sense says you would always connect the ground conductor.

The best thing to do with any unused conductor is to connect it to ground (earth), especially if its in a cable with other conductors which are in use.
 
How does the extractor get it ground and neutral? The neutral must come from the same circuit as the hot.
I can't speak for the rules in the USA but common sense says you would always connect the ground conductor.

The best thing to do with any unused conductor is to connect it to ground (earth), especially if its in a cable with other conductors which are in use.
That’s what I told him Dave
 

Reply to What to do with unneeded NM conductors? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock