sparky351355

i recentley carried out an ecr to a domestic dwelling and found the main earth was sparking when touched to the earth bar, all test result were ok , all ir's to all ccts were +299Mohm , main protective bonding conductors all verified , split board installed (16th) split with 30 mA additional protection and rcbos for lights. TNC-s earthing system. basically no problems, however i seem to be getting 72v from the earth bar to the main earth at the consumer unit. this voltage decreases as i start to turn off each cct all the way down to 0v, ive had the supply checked by DNO all ok. im using a megger mft 1720 test kit , totally bemused by what is happening,> im just wondering wether this is an induced voltage but from where ? any suggestion would be greatly welcome , many thanks.
 
do a pscc and pefc. see if they're the same.

measure voltage with analogue meter.
 
  • Like
Reactions: 1 person
i recentley carried out an ecr to a domestic dwelling and found the main earth was sparking when touched to the earth bar, all test result were ok , all ir's to all ccts were +299Mohm , main protective bonding conductors all verified , split board installed (16th) split with 30 mA additional protection and rcbos for lights. TNC-s earthing system. basically no problems, however i seem to be getting 72v from the earth bar to the main earth at the consumer unit. this voltage decreases as i start to turn off each cct all the way down to 0v, ive had the supply checked by DNO all ok. im using a megger mft 1720 test kit , totally bemused by what is happening,> im just wondering wether this is an induced voltage but from where ? any suggestion would be greatly welcome , many thanks.


You've given yourself the clue already.

as Tel says try it with a proper (!) meter, that isn't affected by induced voltages.

As for "from where" you've probably answered that too, from the live circuits running next to the cpcs .....inducing.......
 
  • Like
Reactions: 1 person
Firstly you should never have the installation live without the earth connected, if this was a commercial or industrial installation there could be a large enough earth current to cause injury or death.

The earth is functional as well as protective so not all earth currents are fault currents.
 
  • Like
Reactions: 1 person
this was an empty property , im well aware of energised ccts and having the main earth disonnected ,the main protective bonding conductors were still connected and the functions of earthing!! there was no current passing so assumed this to be a "phantom voltage"!
 
Yes! repeating Marvo.... why were circuits still live when you were disconnecting the main earth, this is not how you were taught to test; empty property or not.. and in certain set-ups can be potentially lethal to users if not a risk to yourself.
Even when you isolate the circuits you still have to show caution when disconnecting earth as network fault currents can exist, I have come across this twice in 20yrs, once where a neighbouring fault was making metal work live in the property I was in, it was traced to a faulty microwave combined with a breakdown of the DNO earth in the road so using our very good bonding system in part to return as an high impedance fault.
This is why you Isolate circuits and still heed caution as to dangerous voltages.
 
Last edited by a moderator:
...there was no current passing so assumed this to be a "phantom voltage"!

Did you try measuring the current?

Try a clamp meter on the earthing conductor with all connections in place. See what the current is, with the system loaded and unloaded.
 
this was an empty property , im well aware of energised ccts and having the main earth disonnected ,the main protective bonding conductors were still connected and the functions of earthing!! there was no current passing so assumed this to be a "phantom voltage"!
Are you sure about that? How do you account for the 'sparking' you mentioned in your opening post?
 
Yes! repeating Marvo.... why were circuits still live when you were disconnecting the main earth, this is not how you were taught to test; empty property or not.. and in certain set-ups can be potentially lethal to users if not a risk to yourself.
Even when you isolate the circuits you still have to show caution when disconnecting earth as network fault currents can exist, I have come across this twice in 20yrs, once where a neighbouring fault was making metal work live in the property I was in, it was traced to a faulty microwave combined with a breakdown of the DNO earth in the road so using our very good bonding system in part to return as an high impedance fault.
This is why you Isolate circuits and still heed caution as to dangerous voltages.
Tell me about it! I've actually experienced this myself in fact this ground network current was still present when we had a power outage when the sub or part of the sub was down.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Induced voltage?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
sparky351355,
Last reply from
Deleted member 72666,
Replies
10
Views
2,734

Advert