If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Afternoon Gents, just a query regarding volt drop and extending the equipotential zone on a PME in the level 3 design project.

In my design I used a 16mm armoured and the associated volt drop was 5v, this left 1.9 volts for the lighting ring in the summer house. Tutor said not to worry about the feeds volt drop as it was not cumulative and wouldn't effect the lighting circuit. Is this correct, or just leaving it out for sake of simplicity.

Also, if I were to use a 16mm feed, would that also allow the PME to export its earth? The summer house has sinks and toilets so I assume will have copper piping to underground. I can recall seeing a 10mm bond would mitigate the risk but cannot find the appropriate reg with regards to out-buildings. Would a TT earth stake be a better solution?

Thanks for looking this over and look forward to your inputs! :)
 
Would a TT earth stake
yes .that would be correct .
[automerge]1569776441[/automerge]
you can not export the earth just in case you lose the neutral has is combined with the earth.
[automerge]1569777476[/automerge]
disagee mr robinson ?it depends if there is anything in the outbuilding which requires main equipotential bonding, if there isn't a water or gas supply, or structural steelwork, then there is no need to TT the outbuilding. .
[automerge]1569777615[/automerge]
 
Last edited:
  • Disagree
Reactions: Robson689
Quick question: are you sure you need to consider the design of the summer house in the assignment? It's great you're thinking these issues through, and it's possible either (a) the assessment might have changed since I last saw it, or (b) perhaps your tutor set you extra tasks to get you thinking... but just for your own peace of mind, read the assessment questions carefully so you don't end up doing extra work you don't need to.

You need to include the feed to the summer house when determining the maximum demand (with and without diversity), but my recollection is that was the only thing you need consider about the summer house.

Do check, though, I could well be wrong. :)
 
  • Agree
Reactions: Edtwozeronine
No I dont need to do anything to the summer house really, just run a feed to it with a 32amp rcbo. Im just using it as a good exercise to flush out all questions I have in my mind.

So just to wrap my head around the praticalities. 2 core swa (live and neutral), earth the armour at supply end but terminate into whiska or similar without earthing the load side of the armour. Protective bonding pipes to MET in the summer house unit and TT stake.

What are your opinions on the volt drop? Was i correct to size it with consideration to additional at 6.9v total drop or was that over designing it?
 
  • Like
Reactions: happysteve
In considering your thoughts about PME and outbuildings, consider this:

- Where is the main intake/service head? (In the main hotel building)

- Where is the sub-board from which you were going to take a sub-main for the summer house? (In the cafe/pool block)

These are separate buildings. The cafe/pool block isn't on a separate earthing system (TT), according to the design specifications. Would the summer house be any different?
 
  • Like
Reactions: DPG
Tutor said not to worry about the feeds volt drop as it was not cumulative and wouldn't effect the lighting circuit
your tutors is correct .
 
Last edited:
Fair enough if it's a thought experiment, good on you. :)

Volt drop needs to be considered from the origin of the installation, so taking that into account on the sub-main is required, as you've been doing.

On a sub-main, although your limit is 3% (unless there are no lights on the sub-board), usually the majority of the load from the sub-board is general power, only a small portion of the sub-board's load will be for lighting. If you design the lighting to be energy efficient, with fixed loads (that users can't replace with higher loads like halogen lamps), you're likely to be drawing less than an amp for a summer house, and so additional voltage drop on the final lighting circuits isn't going to be a big issue.
[automerge]1569779979[/automerge]
is this a job or on paper ?
It's on paper. It's an assignment on the 2365 level 3 qualification.
 
  • Like
Reactions: buzzlightyear
Fair enough if it's a thought experiment, good on you. :)

Volt drop needs to be considered from the origin of the installation, so taking that into account on the sub-main is required, as you've been doing.

On a sub-main, although your limit is 3% (unless there are no lights on the sub-board), usually the majority of the load from the sub-board is general power, only a small portion of the sub-board's load will be for lighting. If you design the lighting to be energy efficient, with fixed loads (that users can't replace with higher loads like halogen lamps), you're likely to be drawing less than an amp for a summer house, and so additional voltage drop on the final lighting circuits isn't going to be a big issue.
[automerge]1569779979[/automerge]

It's on paper. It's an assignment on the 2365 level 3 qualification.

So, to clarify. Is it 3% volt drop from the sub-main at the summer-house, or at service head? As originally calculated I had a VD of 10/11v from the cafe block alone which left nothing for the lighting ring and the tutor implied this was ok so I got confused.
In considering your thoughts about PME and outbuildings, consider this:

- Where is the main intake/service head? (In the main hotel building)

- Where is the sub-board from which you were going to take a sub-main for the summer house? (In the cafe/pool block)

These are separate buildings. The cafe/pool block isn't on a separate earthing system (TT), according to the design specifications. Would the summer house be any different?

Agreed so this is where I get confused, In what situation is it ok to increase the pme equipotential zone and when does it require TT. Both the cafe block and summerhouse have water supplies and possible extraneous conductive parts... sorry for being annoying it just seems like there are overlapping answers.
 
Volt drop is from the source of supply, it is culmative.

If you have multiple DBs on long circuits and only accounted for volt drop from each DB you’d soon come unstuck. So if you had four DBs in a row and used the maximum permitted on each then you’d potentially be only getting 202 volts at the end of the final circuit.
 
  • Like
Reactions: DPG
[automerge]1569777476[/automerge]
disagee mr robinson ?it depends if there is anything in the outbuilding which requires main equipotential bonding, if there isn't a water or gas supply, or structural steelwork, then there is no need to TT the outbuilding. .
[automerge]1569777615[/automerge]
OP mentions using 16mm SWA price difference between 2 core & 3 core is probably what you'd spend on the earthing materials anyway so what's the point in the TT when you can just extend the equipotential zone and lowest earth resistance possible?
 
mentions using 16mm SWA price difference between 2 core & 3 core is probably what you'd spend on the earthing materials anyway so what's the point in the TT when you can just extend the equipotential zone and lowest earth resistance possible
try reading the guidance note 8 .
 
try reading the guidance note 8 .
I don't have these books, however the Garage-Shed-Supplies.pdf you posted even says it is possible to do what I said?
 
I found I was guilty of over egging the pudding in a lot of my project work, don't make work for yourself innit!
 
I found I was guilty of over egging the pudding in a lot of my project work, don't make work for yourself innit!

Im trying not to but id rather fail on paper and learn than take the easy route and come undone later.

I don't have these books, however the Garage-Shed-Supplies.pdf you posted even says it is possible to do what I said?

As far as my very limited understanding goes. If no extraneous parts then no TT needed, If extraneous parts, TT. Or, you could run a 10mm main protective bond back to the original MET, or, if the orginal supply cable earth Is greater than 10mm and is sized both to provide main protective bonding and CPC functions concurrently, then the PME can be exported using the supply cable.

Or am I way off base? I only had two coffees today so not thinking clearly :D
 
I have put on your post about garages read please.
 
Hi all, Im just starting my design assignment, my query is are we supposed to do all cable calcs for the summerhouse aswell as there is no mention in the question paper about it, only pool and cafe. thx for the help in advance
 
Hi all, Im just starting my design assignment, my query is are we supposed to do all cable calcs for the summerhouse aswell as there is no mention in the question paper about it, only pool and cafe. thx for the help in advance
If there are circuits in the summer house then you will need to design them, so yes, you will need to do the calcs.

TBH once you get into the flow you'll be surprised how quick you can do them.
 
  • Like
Reactions: Petej999

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Gurnatronics

Trainee
~
Joined
Location
Derby
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
2365 Level 3 Design Project. Volt Drop feed to Summer House and earthing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Gurnatronics,
Last reply from
Strima,
Replies
16
Views
8,487

Advert