ian65

Hi every one,
I should know better but can’t get my head round this one and lost my notes from College.
On site guide is saying up to a 9.7Kw shower the cable CSA should be 16mm this seems rather high to me and impossible to work with.
I am fitting a 9.5Kw shower and looking at smaller CSA than 16 probe’s 10 but this will be for an assessment for a company and has to be correct can some one give me the formula for CSA, the fuse to be used are 40Amp and the total run is 11Meters from consumer unit to the shower.

Thanks Ian.
 
Not that your 9.7kW shower is likely to trip it but your shower is theoretically pulling 42A so having it on a 40A breaker doesn't look too good for an assessment. Haven't got any books with me but 6mm clipped direct has a surprisingly high CCC. :)
 
Thanks for your feedback any more please feel free Thanks Ian.
Electricians guide page 52 under : Upto 9.7Kw Shower and thanks i will find my paper work some where prob's in a cupboard
 
Hi and thanks for replying the run is up about 50mm on plastick trunking behind fitted kitchen unit and then to the loft space, this has from what i am told heavey duty lagging but will run over top and then down into a cupboard for switch D/Pole.

I was looking closer at the On site guide and found like a nut i was looking at all the wrong tables untill i got the correct one and i have used Clipped direct method. 2.5 has a 27Amp CCC i am calculating 10 mm should be ample for a 11M run

Thanks Ian.
 
Loft insulation there is and lots of it so i will run it over the top, This is a bungalow i am working in.


Thanks for reply
 
I was looking closer at the On site guide and found like a nut i was looking at all the wrong tables untill i got the correct one and i have used Clipped direct method. 2.5 has a 27Amp CCC i am calculating 10 mm should be ample for a 11M run



I did say I thought you had the wrong table!!! Still wanted to see you terminate 16mm in to a pull cord... that would have been worth watching!!!

Are you "In" currently Ian.... I'll pop round as I'm headed "up the road"!!
 
On the basis you're going to use 10mm cable and that you will be using a pullcord isolator switch, I'd highly recommend the Crabtree 50A isolator.
 
As per Instructions with the shower a 40A fuse is to be used.

Thanks Ian.

As Pushrod has already stated, wouldn't you be better sticking to the regs and using a 45A fuse, rather than following what seems to be the wrong advice in the instructions included with the shower ?

Although the shower manufacturers are probably selling the product as a 9.7Kw unit when in actual fact it is much less :innocent:
That is probably why they are advocating a 40A protective device. Either that or they are numpties.
 
As Pushrod has already stated, wouldn't you be better sticking to the regs and using a 45A fuse, rather than following what seems to be the wrong advice in the instructions included with the shower ?

Although the shower manufacturers are probably selling the product as a 9.7Kw unit when in actual fact it is much less :innocent:
That is probably why they are advocating a 40A protective device. Either that or they are numpties.

Some manufacturers still use 240V instead of 230. The shower is probably rated at 9.5Kw at 240V. 9500 ÷ 240 = 39.6A.
 
James

The shower has a set resistance so the KW rating varies

Use 10 ohms an example
250 devided by 10 = 25 amps
240 " 10 = 24 amps
220 " 10 = 22 amps

Its more the K watt rating that is affected,the current goes up with more voltage
 
James

The shower has a set resistance so the KW rating varies

Use 10 ohms an example
250 devided by 10 = 25 amps
240 " 10 = 24 amps
220 " 10 = 22 amps

Its more the K watt rating that is affected,the current goes up with more voltage

Doh, thanks for clearing that up. Obviosuly getting my Power Triangle and Ohm's law mixed up :innocent: back to the classroom for me.
 
The only theoretical constant is the resistance. Power, current and voltage are all variables. Increase the voltage and you will increase the current and the power. As already mentioned you can still find powers of appliances being calculated on the old 240v (P = V²/R) which would mean a smaller current was flowing. Also a 40A fuse should hold on 44A for an hour [ for an mcb as a guide, 1.12 x In should not trip within an hour and 1.45 x In should trip within an hour]. Personally though, on an assessment i would not want margins to be so close. :)
 
6mm on a 40A more than adequate if clipped direct. never seen a so called 9.5kW shower pull more than 36A.
 
I would use 10mm clipped direct above loft insulation, although 6mm would be ok but 10mm is better if they upgrade the shower at a later date, minimum 45amp breaker or although the norm is to use 50amp. I used to work for a council refurb company and that setup was always used. however i have never seen one over draw 40amp breaker unless you ran it scolding hot for ages. One thing that was always over looked when sparks fitted 50amp breakers that the shower iso was only rated at 45amp. Just some points from my experience
 
Many thanks folks,
for all advice given i will now add a 50 Amp Isolator to the list i was thinking of doing that as well as the pull cord.

From the looks of it the shower isn't going to be put in quite yet so i have some time to play with until the full instal is complete. Am looking to get cables in place though ready for the go ahead.

Cheers every one Ian.
 
Just a passing thought,
I condemd the washing machine last week it took out the RCD and PAT tested it and it failed on Insulation and Earth leakage but they know got all new parts in the machine.

Ian.
 

Reply to 9.5Kw Shower on-site guisde? 16mm Twin & cpc? in the Australia area at ElectriciansForums.net

Similar Threads

Run into this today at a house my nephew is moving into.... Original Dolphin 860 Shower (8600W) installed on 6mm Twin and Earth - maybe 15m...
Replies
4
Views
4K
ELECSA Certification Scheme Regulations Clarification (ELECSA Assesment)
Hi All, I have my ELECSA assessment in a few weeks time. I was going to install an in-line water heater at a friends house but am now considering...
Replies
73
Views
9K
As you may know looking at some of my posts I've been thrown back in the deep end recently – and don’t have much experience with complicated...
Replies
9
Views
4K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
B
Hi Guys, Looking for a little advise regarding installation of new supply to feed a communal shower block at a local Girl Guides Camp. The owners...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock