I’m wavering a bit on this one.
RCD then B10 breaker. 1.5 sq mm 3 core SWA.
That runs underground in ducting, then up and feeds about 10 LED class 2 lights, with cable cleated to the wall, then under again in ducting and about 5 more lights with cable again cleated to the wall.
Now the thing is at the lights SWA glands haven’t been used, just grommets and silicon. I’m not concerned about water ingress as they fit well. But the steel armour isn’t joined anywhere. One core is used as CPC and continuous for whole circuit.
When I mentioned it I was told this came up before and they had got someone to improve it. Then I noticed that in both cases the light at the start of each underground run had been properly glanded with banjos and the armour connected to the CPC. So the two underground sections do have the armour earthed.
I feel like taking a pragmatic view that the bits that matter most are earthed, and the rest of the surface cleated cable could have been NYY-J or anything UV resistant, and it isn’t desperately unsafe that the armour is sitting there unearthed. As before the CPC is continuous (which felt like a miracle in itself with 15 class 2 fittings)
So I’m thinking this is a C3 at worst, mainly for wrong glands. I’m interested if there are safety aspects I’m missing though.