Can anyone please explain what is the maximum earth fault loop impedance permitted for moulded case circuit breaker (MCCB)?
Also, BS 7671 says a disconnection time of 5 sec is allowed for breakers in distribution circuits. What is the difference between a distribution circuit and final circuit?
 
it depends on the rating of the protective device.

a distribution circuit is one that supplys another consumer unit or distribution board.
A final circuit is one that would supply the final equipment ( lighting, motors, appliances ect)
 
distribution circuit is a circuit suppling a c/u sub mains etc
final circuit is a circuit supplying like a light - socket - cooker - motor circuit it does exactly wot it says on the tin final circuit from c/u where it usualy has an end point :cool:
 
Thanks for help about the distribution circuits.

I undrstand that the values of Zs as mentioned in table 41.3 of BS 7671 are the same for MCB and MCCB, is it correct?

Also, Table 41.3 provides Zs for breakers up to 125A only. I need Zs for larger breakers (150A, 200A, 300A, etc). Where can I find Zs for the larger breakers?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earth Fault Impedence
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
Loyal,
Last reply from
pevvers,
Replies
9
Views
4,191

Advert