Maybe too many, or not enough, zeros there! Anyway, does anyone have any idea why a generation meter wouldn't have moved from this number for a few days? It came pre-configured as this (I'm assuming it was tested prior to being sent out).
Also, the generation meter has a constant red light on. I think this may indicate that something isn't right somewhere, but I wasn't supplied with an instruction book for it.
 
Last edited by a moderator:
It's an Elster A100C. I was wondering whether it was wired in wrongly, i.e. The 'Mains' and 'Load' are the wrong way.
 
Will do mate, thanks. I was a bit wary of doing that as I don't want to fry it! I've got the Load side connected to the AC Isolator which feeds into the Inverter. The Mains is going into the Consumer unit. Does this sound right?
 
I've got the Load side connected to the AC Isolator which feeds into the Inverter. The Mains is going into the Consumer unit. Does this sound right?

That's backwards. The consumer unit is the load and the inverter the mains on a PV installation. On the A100C (and others?) if the red light is on constantly it means the meter is trying to 'run backwards' (ie load and mains connected the wrong way round).
 
That's backwards. The consumer unit is the load and the inverter the mains on a PV installation. On the A100C (and others?) if the red light is on constantly it means the meter is trying to 'run backwards' (ie load and mains connected the wrong way round).

That is exactly what i was hoping to hear Julian, thanks. The logic of what you say makes sense, and is just what I was thinking. As I mentioned previously though, I didn't want to risk messing it up and setting fire to something haha. Thanks for that.
 
No probs. Even now I still have to double check when wiring the meter up as I instinctively want to do it the wrong way round!
 
That is exactly what i was hoping to hear Julian, thanks. The logic of what you say makes sense, and is just what I was thinking. As I mentioned previously though, I didn't want to risk messing it up and setting fire to something haha. Thanks for that.


You're not alone we did the same thing with our first install. Poor customer coughed up all that cash and thought it didn't work. Changed the wiring and hey presto it worked!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Generation Meter stuck on 00000000.4
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
GLES,
Last reply from
SRE,
Replies
11
Views
7,450

Advert