I'm currently working on some general improvements and fault rectifications on an unoccupied house, in my spare time. I've found that the living room ring and the kitchen radial are joined, so both remain live when one of the breakers is turned off. I've found the offending connection, problem is I can only disconnect it from the living room circuit as it joined to a socket. At the kitchen circuit end it must feed from a JB which is totally inaccessible, behind kitchen units. I've disconnected from the living room circuit, but obviously this has left live conductors from one circuit in an accessory from another circuit. I left it terminated into a wago connector and taped up, at least for now. I'm not happy with this at all, but can't see an immediate solution, any ideas?
 
put all 3 phase conductors in the DB on 1 20 amp mcb and it will become 1 circuit, you can always then think about rewiring to 2 circuits if the customer gives permission
 
I'm currently working on some general improvements and fault rectifications on an unoccupied house, in my spare time. I've found that the living room ring and the kitchen radial are joined, so both remain live when one of the breakers is turned off. I've found the offending connection, problem is I can only disconnect it from the living room circuit as it joined to a socket. At the kitchen circuit end it must feed from a JB which is totally inaccessible, behind kitchen units. I've disconnected from the living room circuit, but obviously this has left live conductors from one circuit in an accessory from another circuit. I left it terminated into a wago connector and taped up, at least for now. I'm not happy with this at all, but can't see an immediate solution, any ideas?
If you can get to it under the floorboards you could cut it and terminate it into a mf jb there and label what it is, not perfect but better than leaving it in the socket
 
Same as MDJ put it on one MCB, I had this last week in a house, found it when I was testing work I'd done, found that even with the RCD turned off an mcb on the unprotected side made an mcb live on the protected side
 
Rather than reducing to a 20 amp breaker
Incorporate the kitchen sockets into an extended ring by disconnecting the living room ring leg where the extension takes place,then put them all on one 32 amp mcb (if readings permit)
 
Rather than reducing to a 20 amp breaker
Incorporate the kitchen sockets into an extended ring by disconnecting the living room ring leg where the extension takes place,then put them all on one 32 amp mcb (if readings permit)

I had considered this, but it's a non-starter cos I can't get to the end of the kitchen radial without chasing. Kitchen has of course already been decorated. Prats.
 
I am possibly reading the description incorrectly.but how I am picturing the set up and my thoughts

The kitchen loading considered,it would be better for there to be a 32 amp capacity by incorporating what he has in the kitchen into a ring which includes that kitchen
Even if sockets in parts of the rest of the original ring then become their own radial circuit,sort of swapping the problem from the kitchen where high loads need satisfying, to the rest of the house where low loads are not such a problem
As he stated though,it can't be done,whther I see the picture or have blurred vision lol
 
That is good thinking
[ElectriciansForums.net] Joined circuits


I have been scrummaging,(I meant rummaging ) around for answers,but I think I need lineout ( sorry again,I mean timeout) to get myself converted to the idea
[ElectriciansForums.net] Joined circuits
 

Reply to Joined circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
I recommend the Manrose Humidistat timer: Humidity Sensors for fans -...
Replies
1
Views
953
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...
Replies
13
Views
3K
By code the washing machine needs its own 20 amp single pole GFCI circuit, the dryer needs a 30 amp double pole breaker and using # 10 wire. Your...
Replies
1
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks