Okay, I know this has been discussed extensively elsewhere but I think this deserves another thread.
Seeing as we have generally come to a consensus that RCDs intended to provide ADS may still be being supplied from the LOAD side by the inverter, perhaps as much as 5s after the RCD has operated, this seems to me to throw up an important problem.
For installations where RCDs are required, we therefore won't be able to provide ADS on a circuit without additional protection. It is my thinking that the only way we could provide such a thing would be by installing a seperate RCD at the inverter. Unless I am missing something?
Seeing as we have generally come to a consensus that RCDs intended to provide ADS may still be being supplied from the LOAD side by the inverter, perhaps as much as 5s after the RCD has operated, this seems to me to throw up an important problem.
For installations where RCDs are required, we therefore won't be able to provide ADS on a circuit without additional protection. It is my thinking that the only way we could provide such a thing would be by installing a seperate RCD at the inverter. Unless I am missing something?