Anyone who decides to fit one of these Vphase units to an already installed dual RCD board, I wish you all the luck in the world.


They only work for certain circuits right, so how the hell do you reconfigure a dual RCD CU so circuits are still split across both RCDs properly then fed via a Vphase.

Not easily I think
 
I reckon the only sensible way to run them would be to get a small split board fed solely from the vphase, but the incomers on the units won't accept tails so you'd need to fit a dedicated circuit in the old board and use a bit of 16mm.

So, more initial configuration expense, even longer payback.

In fairness to vPhase, they do say that the best time to fit one is when replacing the CU.
 
I reckon the only sensible way to run them would be to get a small split board fed solely from the vphase, but the incomers on the units won't accept tails so you'd need to fit a dedicated circuit in the old board and use a bit of 16mm.

So, more initial configuration expense, even longer payback.

In fairness to vPhase, they do say that the best time to fit one is when replacing the CU.

I reckon the only sensible way, ...is to stay well clear of these Vphase units, Full Stop!!!
 
I reckon the only sensible way, ...is to stay well clear of these Vphase units, Full Stop!!!

I don't hear anyone on here disagreeing with you, least of all me!
 
Unless I’m very much mistaken I think the members of this board have christened the VPhase an unmitigated impractical failure.

I’ll happily read any evidence to the contrary, and if substantiated data is given I’ll review my opinion.
You all know I have nothing to gain or loose with these units, as with most things I stand on the sidelines and offer advise when I can. My advise on this one is save the unit and installation costs by keeping your money in your pocket. 100% recovery of installation costs instantly.

PS I don’t rate them:death:
 
Last edited by a moderator:
"As seen on TV". So were my mum's pot plants.
 
"As seen on TV".

So have a lot of other products that failed or never made it to market, you only need to look at Dragons Den a lot appear never to be seen again

And vphase doesn't defend it now on the forum, so does his silence speak volumes for the product ?
 
For goodness sake don’t rattle his cage you’ll wake him.

I was only wondering how these vphase units optimise the voltage at 220v if the supply voltage was lower than 220v but I think he may now be trying to sell sand to the arabs:21: due to his lack of response
 
I was only wondering how these vphase units optimise the voltage at 220v if the supply voltage was lower than 220v but I think he may now be trying to sell sand to the arabs:21: due to his lack of response

Completely unrelated to this thread subject but...... You would be surprised at the enormous amount of sand that IS sold to the Arabs countries. The sand they have in abundance, is totally unsuitable for building purposes, it's more of a chemical rich dust, than actual sand... lol!!
 
I have a bottle of Sahara Desert from a trip one time, and yes, it's more like flour than sand!
 
I was only wondering how these vphase units optimise the voltage at 220v if the supply voltage was lower than 220v but I think he may now be trying to sell sand to the arabs:21: due to his lack of response

Perhaps he has given up trying to educate idiots it is pretty obvious that if your supply voltage is less than 220v it wont benefit from being reduced.
 
Then more fool them, The V phase domestic unit is of little use to man nor beast. Expensive to buy, expensive and complicated to install, and pay back times are abysmal, as it runs more on the by-pass mode, than it does on what it was installed for, ....saving money mode!!
 
These days the management of a lot of organisations are non technical bean counters who will buy into an idea if they think it will save money and increase their bonus. Is it any surprise that some people are suckered in to buying this technology without considering the evidence and the facts or the lack of them
 
Then more fool them, The V phase domestic unit is of little use to man nor beast. Expensive to buy, expensive and complicated to install, and pay back times are abysmal, as it runs more on the by-pass mode, than it does on what it was installed for, ....saving money mode!!

Im an electrician and have brought one of these units (oh no I'm a defector) to have a play with, my main intention is to protect my equipment. Which is one point not mentioned here much..
Surely this unit has much more value in the fact it could be a life line to all your interconnected equipment.
Most of our equipment is designed around a European voltage and all those switch mode drivers in my precious led lights don't like 253v intravenously injected into its backside. Other things like laptop and computer power supply's, cfl lighting, central heating controllers etc will run cooler and last longer Cfls fail because they run to hot and the fridge is surely working harder than it needs too..

Could be the best £60 I've spent!
 
Im an electrician and have brought one of these units (oh no I'm a defector) to have a play with, my main intention is to protect my equipment. Which is one point not mentioned here much..
Surely this unit has much more value in the fact it could be a life line to all your interconnected equipment.
Most of our equipment is designed around a European voltage and all those switch mode drivers in my precious led lights don't like 253v intravenously injected into its backside. Other things like laptop and computer power supply's, cfl lighting, central heating controllers etc will run cooler and last longer Cfls fail because they run to hot and the fridge is surely working harder than it needs too..

Could be the best £60 I've spent!

Except when it goes into bypass mode above 20A,
 
Just had another thought, we go to all the trouble of calculating Volt drop (albeit at 230) and then introduce a whopping circa 20V drop at the origin with one of these devices.

Just a thought, hmm.
 
Except when it goes into bypass mode above 20A,

Which will be like never... Hopefully.
Ill just use it on lights and general power and even if we use above 4kw r It won't be for long.

If I could get them all for £60 I'd even think about offering them to my customers, just for points mentioned about equipment protection let alone the (supposed) benefits of saving energy.

I brought it cash through eBay (brand new no box)

Not sure how well it regulates the 220v but looking at the components used it's pretty well made.
 
£60 is cheap for peace of mind knowing my down lights are not going to pop all over the house. The boiler control board cost me £130 so if it stops that from blowing up I'd be happy too.
And it certainly isn't crap from the components inside, I work (sub contract) for a transformer manufacturing company and understand a little about transformers and how expensive they can be.
 
Last edited by a moderator:
£60 is cheap for peace of mind knowing my down lights are not going to pop all over the house. The boiler control board cost me £130 so if it stops that from blowing up I'd be happy too.
And it certainly isn't crap from the components inside, I work (sub contract) for a transformer manufacturing company and understand a little about transformer design.


If you say so!! ...lol!!
 
Capital C or not, I couldn't careless let's see if it works at saving my equipment.
Then I'll judge.

How are you going to prove that if you don't mind me asking, are you going to run identical equipment from this unit and some direct as a control ?
How big is your sample ?

Are you expecting multiple equipment failure on a regular basis ?
 
They went bust all because of you guys lol
my method of control is:
does my stuff work for the next 25years with this thing interconnected...?

ill let you know in a 1/4 of a century.
 
They went bust all because of you guys lol
my method of control is:
does my stuff work for the next 25years with this thing interconnected...?

ill let you know in a 1/4 of a century.

Like anybody takes any notice of us lol

No, they went bust by trying to sell snake oil and bending the laws of physics, which we tried to tell them.

Seriously though, if they were any good they would have made a fortune, particularly with energy costs these days and the current economic climate (pardon the pun)
 
They went bust all because of you guys lol
my method of control is:
does my stuff work for the next 25years with this thing interconnected...?

ill let you know in a 1/4 of a century.

How will you know that this unit saved your equipment or that early failure without it was just normal wear and tear
 
Says it all really. Someone wanted to get rid of it.
Client went bust apparently.
How else do you suppose I protect my equipment then? With an off the self product that won't make my insurance invalid if my house burns down?
my purchase being slagged off an all...
 
If you're happy spending £60 plus the time and effort installing it, I'm very happy for you.
All I can add is that my computers, hifi, lamps, combi etc etc seem to have functioned perfectly fine for the last 20 odd years running off the crude mains! :)
 
Client went bust apparently.
How else do you suppose I protect my equipment then? With an off the self product that won't make my insurance invalid if my house burns down?
my purchase being slagged off an all...

If it isn't on off the shelf product that you have bought what is it

Personally I think you are barking just not sure which tree these VPhase things are just like the kings new clothes you have been sold an idea that is not all it seems and cannot meet the claims made for it
 
It'll take me about 15mins to install and cost £60 and I'm barking?
problem:
incoming supply voltage 251v
We have things blowing up or not lasting like led drivers.
Solution?
 
It'll take me about 15mins to install and cost £60 and I'm barking?
problem:
incoming supply voltage 251v
We have things blowing up or not lasting like led drivers.
Solution?

15 mins, i think not?? Not if you install it, as per manufactures instructions it won't!! lol!!
 
Never mind home PC’s. For 35 years I’ve had PC’s at work on a 433/250V system. Terrible harmonic distortion when a 400HP motor starts DOL.

Funny thing, I’ve never had one fail, I wonder why? Most died of old age, like me!

I’m not writing all my finding on voltage reduction again, use the search function.
 
Never mind home PC’s. For 35 years I’ve had PC’s at work on a 433/250V system. Terrible harmonic distortion when a 400HP motor starts DOL.

Funny thing, I’ve never had one fail, I wonder why? Most died of old age, like me!

I’m not writing all my finding on voltage reduction again, use the search function.




Jesus i still can't get any of you to see my perspective of this.. Ive not been sucked into any gimmick I didn't even realise these things were available until the Elecsa inspection on Monday. Got talking to the assessor about what options I had...

REPEAT ITS NOT ABOUT SAVING MONEY ON MY BILL!


You want me to remove before I've even installed it.. At least let me see if my lights work!
yes it'll take me 15mins possibly less. I could even part p it online and have time to spare. (Although I've not looked at the instructions) it's still 15mins I've not got (the joys of becoming a dad)


Also not that I brought it for my PC but most psu's for desktops are well designed and built, but some switch mode psu's for laptop's they don't like the extra heat 250v brings!


Anyway im out, I was only suggesting a specific point of use for this piece of Crap that seemed to have been missed in theoriginal post about the product.


All you you haters be haters and enjoy your life!
ill do it at 220v for £60 and he hated till the cows come home if my beloved led down lights keep working.
 
Just do it!

You’ve convinced yourself it will improve things so I doubt we’ll get a reasoned argument for or against.

To get realistic results you need to conduct the test over several years. The big problem is creating a baseline comparison.




TnT developments will handle the sales. Trev deals with the smoke and mirrors, I sell the snake oil. We’ve been doing it for years!
 
Just do it!

You’ve convinced yourself it will improve things so I doubt we’ll get a reasoned argument for or against.

To get realistic results you need to conduct the test over several years. The big problem is creating a baseline comparison.




TnT developments will handle the sales. Trev deals with the smoke and mirrors, I sell the snake oil. We’ve been doing it for years!

Still not one solution to my problem. Just an argument against this product.
The comparrison will be: no faulty equipment - happy man and I get to say told you so! If it don't then your welcome to buy it off me for your wall of Crappy fame.

So what I'll do is listen to you guys, I'll not fit it cause its crap sorry Crap, I'll then continue to have my equipment go faulty. I'll tell the mrs not to worry about the boiler control panel blowing up again cause you guys know it's not worth fitting a Crap product like this to protect it.

Forum closets gotta love em.

i should become a plumber they have no-directional thought patterns.
 
yes it'll take me 15mins possibly less. I could even part p it online and have time to spare. (Although I've not looked at the instructions) it's still 15mins I've not got (the joys of becoming a dad)


If you install the VPhase AS per manufacturers instructions, then i'll put money on you not installing it in 15 mins. But it sounds that you know best, right!! You do know i take it, that the Vphase unit is not just connected to supply the whole CU dont you?? You seem to want to make an argument for a bit of kit you've only just heard about.

I hope it works for you, i really do!! But as far as i can tell you'll really never know for sure. But i suppose if nothing happens to your equipment one way or the other, you'll convince yourself you were right anyway!! lol!!
 
I better have a look at the instructions then.. Surely 4screws a bit of 16mm tails and a 50a breaker can't possibly take much longer unless I get the plumber to do it?

I'm sure we will know in the first few years, if we don't replace any equipment, that's enough for us. Regardless of really knowing for sure if it works. (Which I'd say it was if so)
 
Btw I wasn't making an argument for it I was just trying to get someone to give me a better solution as soon as my purchase got slagged off.
 
I think if things were being damaged and the supply voltage was close to the upper supply level allowed I would be contacting the DNO for them to check, had this before where the DNO had a fault on the local network because auto tapping transformers were not set up properly

A few years ago a mate of mine who lives in a rural area had various electrical items damaged including 3 microwaves. He borrowed some monitoring kit from where he works and found that he was periodically getting voltage spikes of up to 1000v lasting for a few cycles, DNO put their own monitoring equipment in but it was not sensitive enough although they did act on my mates evidence and did find the fault and paid for the damaged equipment and some compensation

No need for one of these silly boxes
 
I think if things were being damaged and the supply voltage was close to the upper supply level allowed I would be contacting the DNO for them to check, had this before where the DNO had a fault on the local network because auto tapping transformers were not set up properly

A few years ago a mate of mine who lives in a rural area had various electrical items damaged including 3 microwaves. He borrowed some monitoring kit from where he works and found that he was periodically getting voltage spikes of up to 1000v lasting for a few cycles, DNO put their own monitoring equipment in but it was not sensitive enough although they did act on my mates evidence and did find the fault and paid for the damaged equipment and some compensation

No need for one of these silly boxes



I have spoke to central networks who have
had it monitored, it falls within specification. Obviously I can't be sure if they are telling the truth.

I used to work for a company employed by all the distributors testing consumers installations after distributor neutral faults, but before re-energizing. The fault usually blowing up all equipment connected to the network. As you will know this type of fault causes high voltage spikes, I'd also be repairing peoples blown VDR's in essential equipment to get back on. Other operatives from the company would collect all the faulty equipment and take it back to our office to either be repaired or replaced. Horrible job.

still not fitted it, looked at instruction manual though it is a bit **** it can only handle 8amps continuous. Still a 15min job plus tea and biscuits exactly how I imagined if even easier 50amp MCB feeding unit in 10mm then back feeding my second RCD in cu with a couple of circuits to re-arrange to feed single rcbos
 
still not fitted it, looked at instruction manual though it is a bit **** it can only handle 8amps continuous. Still a 15min job plus tea and biscuits exactly how I imagined if even easier 50amp MCB feeding unit in 10mm then back feeding my second RCD in cu with a couple of circuits to re-arrange to feed single rcbos

Like you've been told, ....a heap of Crap!! Still think less than 15 mins then, sounds like it's going to be a butchers job!! ...lol!!
 

Reply to Advice on V Phase Voltage Optimisation Units in the Australia area at ElectriciansForums.net

Similar Threads

I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K
Hi all. I am looking for some advice. I am looking to become certified to install consumption measuring devices in small businesses. I have many...
Replies
10
Views
2K
Hi, Thanks to anyone who reads this and offers any advice. Sold my house and the buyer requested an electrical inspection report which they...
Replies
40
Views
5K
Hello Hope your staying safe and well with Covid-19 I am wondering if someone could confirm this for me. I have seen these Single Phase EV...
Replies
4
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock