T

Tommyl

Hi All
I need help with completing EIC. The section i cant quite grasp is where for asks for particulars of installation referred to in certificate. I am installing 2 new radial circuits but not sure what to fill in on form. Im working on a large job where the origin is fed from a 3000A ACB that suppies a LV panel, that panel then supplies numerous DB's. The DB my circuits are connected to is way downstream. Do i put details on the DB im connected to or at main LV panel. Hope i have explained correctly. Thanks
 
Ze and PSCC at origin. Zdb at the DB you are connecting to.
 
main isolator is the one at the DB you connect to as that is the main isolator for your work.
 
Just to add to Tommy’s original post, when recording the main earthing conductor size could it be the main earthing conductor for the entire installation ie connecting to electrode or other means of earthing? Or could it be the main earth connected to the MET of the DB referred to in the installation certificate?
 
Just to add to Tommy’s original post, when recording the main earthing conductor size could it be the main earthing conductor for the entire installation ie connecting to electrode or other means of earthing? Or could it be the main earth connected to the MET of the DB referred to in the installation certificate?
anyone got the answer?
 
It is the earthing conductor for the installation.
 
The existing (at origin) or the new (my install)?
You generally only have one earthing conductor everything else is a cpc or bonding conductor.
 
  • Like
Reactions: nicebutdim and DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EIC particulars of installation referred to in certificate
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Tommyl,
Last reply from
westward10,
Replies
9
Views
9,541

Advert