Hi,
i'm currently working on a project where 10 flats are being built on one side of an old silk mill. We are having a new cable put in and the origin upgraded etc. This type of work has to be done by NERS registered electricians so an outside company recommended by the DNO came yesterday and asked for what each flat will be using current wise so they can do a cable calc for the supply, which is the following.
Boiler 9kw 50am breaker, ring 32a, ring 32a, oven 6.2kw 32a, heating 20a, lights 6a
This is then multiplied by 10 for the ten flats. Looking at diversity tables theres a strong possibility diversity cant be applied unless we could use column 2, heating & power - If not the cable size is going to be ridiculous as it needs to be in trunking, ratings go down etc.. What are peoples thoughts?
 

Intoelectrics

Regular EF Member
Messages
246
Location
Midlands
Is the incoming supply going to be 3 phase? if so the loads will be split over each phase so roughly 3.5 flats per phase.
Also you state that there is going to be 2 x RFC per flat?
 
Last edited:

snowhead

Respected Member
Mentor
Trainee Access
Messages
3,784
Location
Mildlands
Boiler 9kw 50am breaker, ring 32a, ring 32a, oven 6.2kw 32a, heating 20a, lights 6a
If you're using those figures as is, then;

I wouldn't want to pay the electric bill for any of those flats.
And I wouldn't want to be inside any of them with all the excess heat from those appliances running flat out 24/7.

I'm sure the NERS guys are sitting down somewhere chuckling to themselves.
 

MDJ

The Muppet Police
Mentor
Electrician's Arms
Trainee Access
Messages
1,280
Location
Gloucester
Is the incoming supply going to be 3 phase? if so the loads will be split over each phase so roughly 3.5 flats per phase.
Also you state that there is going to be 2 x RFC per flat?
There can be 6 rings, irrelevent
 
  • Like
Reactions: DPG

MDJ

The Muppet Police
Mentor
Electrician's Arms
Trainee Access
Messages
1,280
Location
Gloucester
There is only so much that can be plugged in, a basic flat next to nothing
 

Spoon

Mentor
Electrician's Arms
Trainee Access
Messages
7,879
Location
Lancashire
Boiler 9kw 50am breaker, ring 32a, ring 32a, oven 6.2kw 32a, heating 20a, lights 6a

Out of curiosity, who specified this equipment?
 

Spoon

Mentor
Electrician's Arms
Trainee Access
Messages
7,879
Location
Lancashire
OP
W

Webby

EF Member
Messages
10
Location
Macclesfield
Sorry, I should have been more clear.



Who specified that the flats should have the above?
its an old mill and they didnt want to, or couldnt put gas in so the plumbers themselves will have supplied the boiler, like the kitchen fitters the oven/hob etc..
 

Spoon

Mentor
Electrician's Arms
Trainee Access
Messages
7,879
Location
Lancashire
its an old mill and they didnt want to, or couldnt put gas in so the plumbers themselves will have supplied the boiler, like the kitchen fitters the oven/hob etc..
Ok, so the boiler & oven/hob are already fitted?
 

davesparks

Mentor
Electrician's Arms
Trainee Access
Messages
13,305
Location
guildford
Boiler 9kw 50am breaker, ring 32a, ring 32a, oven 6.2kw 32a, heating 20a, lights 6a
This is then multiplied by 10 for the ten flats. Looking at diversity tables theres a strong possibility diversity cant be applied unless we could use column 2, heating & power - If not the cable size is going to be ridiculous as it needs to be in trunking, ratings go down etc.. What are peoples thoughts?
Why do you say there's a strong possibility diversity can't be applied? Over 10 dwellings diversity can definately be applied!
Your loadings seem very odd to me, it's almost as if you've counted the ratings of circuit breakers instead of actually calculating Ib.

If you've got a 9kW boiler why do you need another 20A circuit for heating?
 

Rob

Control System Engineer
Electrician's Arms
Messages
2,739
Location
UK/USA
I think you need a better electrical contractor.

Although diversity for a block of flats isn't exactly beginner stuff, the information you have provided (I presume has been provided by you by the contractor you've employed) is pretty duff.
 
OP
W

Webby

EF Member
Messages
10
Location
Macclesfield
Why do you say there's a strong possibility diversity can't be applied? Over 10 dwellings diversity can definately be applied!
Your loadings seem very odd to me, it's almost as if you've counted the ratings of circuit breakers instead of actually calculating Ib.

If you've got a 9kW boiler why do you need another 20A circuit for heating?
they are breaker ratings and the 20a for heating is just a radial going to a potterton economy 7 controller for controlling the boiler. I wondered if there was a diversity figure you could apply to there being 10 flats, its not something i have seen as yet though, thanks for the reply
 
OP
W

Webby

EF Member
Messages
10
Location
Macclesfield
I think you need a better electrical contractor.

Although diversity for a block of flats isn't exactly beginner stuff, the information you have provided (I presume has been provided by you by the contractor you've employed) is pretty duff.
According to you it is...
 

davesparks

Mentor
Electrician's Arms
Trainee Access
Messages
13,305
Location
guildford
they are breaker ratings and the 20a for heating is just a radial going to a potterton economy 7 controller for controlling the boiler. I wondered if there was a diversity figure you could apply to there being 10 flats, its not something i have seen as yet though, thanks for the reply
Then you need to use the design current, not the mcb ratings, the reason for this is hopefully obvious.
This 20A heating circuit is a good example, it has a 20A mcb but the only thing connected to it is a timeswitch which will use a fraction of an amp. Over 10 flats that's 200A if you add up the mcb ratings, or maybe 2A if you add up the actual load.
 

Intoelectrics

Regular EF Member
Messages
246
Location
Midlands
There can be 6 rings, irrelevent
Never said it was,

I was just curious... i.e I assumed one for the general sockets throughout the flat and one for the kitchen? Is it a bedsit type flat...etc? I was hinting at the design spec of the install. :rolleyes:
 

Spoon

Mentor
Electrician's Arms
Trainee Access
Messages
7,879
Location
Lancashire
Its ok, i have sorted it, thanks for mostly everyones helpful replies
Glad you got it sorted mate.
Next time it would be better to chat to an electrician and you can go through the design and what is needed together, rather than just bypassing them.
Every day a learning day...
 